trianco oil boiler tro 12/14
Reply with quote Thanks

Seem to have developed a fault on my boiler in the last couple of days,Typical now its gone cold!. Boiler fires every time, runs for about 4 mins and then shuts off(flame only, fan runs on for 15 secs then stops)and then the lockout light comes on. Wait for a minute reset the lockout and the boiler will fire and run for another 4 mins. Would appear to be fuel starvation?,but the tank is 1/3 full(cleaned and checked the sight gauge)cleaned and refitted the bowl filter and plenty of fuel runs through fitting. but the system does appear to have a none return valve fitted, but this seems? to be okay.
Any suggestions hints or ideas would be gratefully received,before we start freezing up.
thanks marko icon_sad.gif
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Terrywookfit

from Antarctica

Joined: 19 Jul 2007
Posts: 1003
Location: Antarctica
Thanked: 9 times

PostPosted: Wed Oct 24, 2007 1:16 am    Post Subject:
Reply with quote Thanks

Check resistance of the solenoid coil immediately after lockout it should be a few K!!
Back to top
 Alert Moderators
markojonah

from United Kingdom

Joined: 23 Oct 2007
Posts: 2
Location: Norfolk,
United Kingdom
Thanked: 0 times

PostPosted: Wed Oct 24, 2007 5:02 pm    Post Subject:
boiler fault
Reply with quote Thanks

having looked at the solenoid coil found that when the boiler locked out thre was no resistane across the coil(i.e. open circuit)when the coil coled down the resistance came back upto 2.8Kohms. new coil orderedand shold be here on friday
Many thanks for the sound advice, very grateful
thanks marko and family
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Air lock in the oil supply line,Trianco Redfyre boiler 14 980 Fri Feb 08, 2008 7:32 am
Trianco oil boiler 15/19 8 680 Mon Feb 04, 2008 9:48 pm
Trianco oil boiler won't fire 22 500 Sun Sep 20, 2009 11:58 am
trianco boiler 11 680 Fri Oct 09, 2009 6:43 pm
Trianco Redfyre 15/19 oil boiler 2 640 Fri Mar 14, 2008 9:01 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.