weather compensator or not?

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
robsant

from United Kingdom

Joined: 07 Aug 2007
Posts: 19
Location: United Kingdom

PostPosted: Mon Apr 21, 2008 8:38 pm Reply with quote

I have been advised to have a Vaillant Ecotec Plus 937. Should i make sure the Vaillant VRC 400 weather compensator is fitted at the same time?

The boiler will be in the center of the house, so not near an outside wall, so will that make it difficult to fit the outside sensor? i guess it could go to the roof where the flu will go but that is 4 meters away vertically.

Finally please can someone explain exactly what the weather compensator does.

Thanks,

Rob
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
WDIK

from United Kingdom

Joined: 15 Dec 2007
Posts: 4864
Location: Nottingham,
United Kingdom
Thanked: 55 times

PostPosted: Mon Apr 21, 2008 9:24 pm Reply with quote

a compensator looks at the room temp, the outside temp and the set temp.
it the then calculates usually by learning from the Q factor of your home just what temperature to have the flow at using a multi variable algorithm based on learned data, as to how long it takes your home to achieve the set point.
in doing this it will instruct your burner to modulate till the desired flow setpoint is achieved.
in buildings with a very high Q often the outside sensor has little value.
optimisation is achieved by switching off in advance on a precalculated drop of say 1/2 degree in the last hr, and switching on to achieve a set temp at the set time according to inside and outside temp.
gives greater climatic control of both comfort and efficiency.
Back to top
 Alert Moderators
howy1

from United Kingdom

Joined: 20 Oct 2006
Posts: 300
Location: Norwich,
United Kingdom
Thanked: 1 time

PostPosted: Mon Apr 21, 2008 9:29 pm Reply with quote

Hello , i had a weather compensator installed with my boiler and i am not convinced it was a good route to go , the other day it was 11 degrees outside and my rads were red hot , also i expected better gas bills but they have not materialised . You dont feel like you have any control of the system as an end user either , so tred carefully .
Back to top
 Alert Moderators
WDIK

from United Kingdom

Joined: 15 Dec 2007
Posts: 4864
Location: Nottingham,
United Kingdom
Thanked: 55 times

PostPosted: Mon Apr 21, 2008 9:31 pm Reply with quote

howy1 wrote:
Hello , i had a weather compensator installed with my boiler and i am not convinced it was a good route to go , the other day it was 11 degrees outside and my rads were red hot , also i expected better gas bills but they have not materialised . You dont feel like you have any control of the system as an end user either , so tred carefully .

usually that because its been set up incorrectly

they do work they are my bread and butter icon_wink.gif
Back to top
 Alert Moderators
simond

from United Kingdom

Joined: 26 Oct 2004
Posts: 4066
Location: Surrey,
United Kingdom
Thanked: 272 times

PostPosted: Mon Apr 21, 2008 9:37 pm Reply with quote

Weather Comp varies the flow temp of the radiator water based upon the outside temperature.

The ratio between the two is set by a multiplier, based upon the insulation value of the property.

There is also an algorithm as the response is not linear, but we don't need to understand this. Some WC allow you to change the curve of the response.

If your property is uniformly insulated (either well or badly) WC can save energy by running the boiler in condensing mode for longer periods.

The Vaillant VRC430 is the new WC controller, the old VRC400 is a pain to use. The distance of the sensor is not too much of an issue as long as the cable is sized to prevent a significant volt drop.

The respondent saying his WC is no good will have the wrong response curve set in the memory, or a house with widely varying insulation values across different rooms.


Last edited by simond on Mon Apr 21, 2008 9:38 pm, edited 1 time in total
Back to top
 Alert Moderators
tonybhoy

from United Kingdom

Joined: 15 Jan 2008
Posts: 7383
Location: Glasgow,
United Kingdom
Thanked: 999 times

PostPosted: Mon Apr 21, 2008 9:37 pm Reply with quote

WDIK wrote:
howy1 wrote:
Hello , i had a weather compensator installed with my boiler and i am not convinced it was a good route to go , the other day it was 11 degrees outside and my rads were red hot , also i expected better gas bills but they have not materialised . You dont feel like you have any control of the system as an end user either , so tred carefully .

usually that because its been set up incorrectly

they do work they are my bread and butter icon_wink.gif


Been trying to push them on Valliants but people don't like the sound of them running the heating system.

Personally I would have one in a minute,anything that can save even more money on fuel bills is got to be worth considering.


However WB CDIs are not set up for them software wise according WB tech.Not that I have a WB CDI icon_lol.gif
Back to top
 Alert Moderators
WDIK

from United Kingdom

Joined: 15 Dec 2007
Posts: 4864
Location: Nottingham,
United Kingdom
Thanked: 55 times

PostPosted: Mon Apr 21, 2008 9:49 pm Reply with quote

tonybhoy wrote:
WDIK wrote:
howy1 wrote:
Hello , i had a weather compensator installed with my boiler and i am not convinced it was a good route to go , the other day it was 11 degrees outside and my rads were red hot , also i expected better gas bills but they have not materialised . You dont feel like you have any control of the system as an end user either , so tred carefully .

usually that because its been set up incorrectly

they do work they are my bread and butter icon_wink.gif


Been trying to push them on Valliants but people don't like the sound of them running the heating system.

Personally I would have one in a minute,anything that can save even more money on fuel bills is got to be worth considering.


However WB CDIs are not set up for them software wise according WB tech.Not that I have a WB CDI icon_lol.gif


personally i have a 2005 greenstar 30he wonder if you can tell me, i fitted the tr2 room sensor and remote, it has its own opt comp, does it allow an outside sensor? is it a 10k?

sorry the wife lost the manual icon_redface.gif
Back to top
 Alert Moderators
howy1

from United Kingdom

Joined: 20 Oct 2006
Posts: 300
Location: Norwich,
United Kingdom
Thanked: 1 time

PostPosted: Mon Apr 21, 2008 9:50 pm Reply with quote

Simond , maybe you summed it up when saying there are wide variations in insulation , house`s especially older ones may not be condusive to WC .
Back to top
 Alert Moderators
WDIK

from United Kingdom

Joined: 15 Dec 2007
Posts: 4864
Location: Nottingham,
United Kingdom
Thanked: 55 times

PostPosted: Mon Apr 21, 2008 9:53 pm Reply with quote

howy1 wrote:
Simond , maybe you summed it up when saying there are wide variations in insulation , house`s especially older ones may not be condusive to WC .


that the Q
Back to top
 Alert Moderators
tonybhoy

from United Kingdom

Joined: 15 Jan 2008
Posts: 7383
Location: Glasgow,
United Kingdom
Thanked: 999 times

PostPosted: Mon Apr 21, 2008 10:00 pm Reply with quote

WDIK wrote:
tonybhoy wrote:
WDIK wrote:
howy1 wrote:
Hello , i had a weather compensator installed with my boiler and i am not convinced it was a good route to go , the other day it was 11 degrees outside and my rads were red hot , also i expected better gas bills but they have not materialised . You dont feel like you have any control of the system as an end user either , so tred carefully .

usually that because its been set up incorrectly

they do work they are my bread and butter icon_wink.gif


Been trying to push them on Valliants but people don't like the sound of them running the heating system.

Personally I would have one in a minute,anything that can save even more money on fuel bills is got to be worth considering.


However WB CDIs are not set up for them software wise according WB tech.Not that I have a WB CDI icon_lol.gif


personally i have a 2005 greenstar 30he wonder if you can tell me, i fitted the tr2 room sensor and remote, it has its own opt comp, does it allow an outside sensor? is it a 10k?

sorry the wife lost the manual icon_redface.gif


WB don't do WC according to their tech guys.

Apparently the PCBs on WB don't have software written that allows WC and according to WB there is no demand for it icon_eek.gif

Give them a phone and ask,

01905754624
Back to top
 Alert Moderators
WDIK

from United Kingdom

Joined: 15 Dec 2007
Posts: 4864
Location: Nottingham,
United Kingdom
Thanked: 55 times

PostPosted: Mon Apr 21, 2008 10:05 pm Reply with quote

then i just have a compensator wb
Back to top
 Alert Moderators
WDIK

from United Kingdom

Joined: 15 Dec 2007
Posts: 4864
Location: Nottingham,
United Kingdom
Thanked: 55 times

PostPosted: Mon Apr 21, 2008 10:06 pm Reply with quote

if you need or want an opt comp have a few coster units kicking around icon_wink.gif
955 611's
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 18693
Location: Bath,
United Kingdom
Thanked: 1486 times

PostPosted: Mon Apr 21, 2008 11:11 pm Reply with quote

Servowarn (honeywell) have been making WC's for years, mine is 26 + and has saved thousands on the fuel bill

Highly recommend if your guy knows how to set them up.
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8487
Location: Sussex,
United Kingdom
Thanked: 974 times

PostPosted: Tue Apr 22, 2008 10:42 am Reply with quote

WDIK wrote:
a compensator looks at the room temp, the outside temp and the set temp.
it the then calculates usually by learning from the Q factor of your home just what temperature to have the flow at using a multi variable algorithm based on learned data, as to how long it takes your home to achieve the set point.
in doing this it will instruct your burner to modulate till the desired flow setpoint is achieved.
in buildings with a very high Q often the outside sensor has little value.
optimisation is achieved by switching off in advance on a precalculated drop of say 1/2 degree in the last hr, and switching on to achieve a set temp at the set time according to inside and outside temp.
gives greater climatic control of both comfort and efficiency.

Q Factor is a new term to me in relation to buildings. I know what is meant by the Q of a tuned circuit in Electronics; but can't see how this can be applied to a building.

Please enlighten me. icon_confused.gif
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52149
Location: London,
United Kingdom
Thanked: 3251 times

PostPosted: Tue Apr 22, 2008 11:05 am Reply with quote

I have not heard that term used for buildings but is quite a good analogy to a tuned circuit.

It is in "simple terms" related to the thermal mass of the building, the radiator output power and the heat loss of the building.

Easier to "learn" than calculate!

Tony
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Weather compensator and efficiency regs 25 1920 Sat Nov 22, 2008 12:19 pm
Viessmann boiler with weather compensator. 25 5060 Sat Oct 04, 2008 4:31 pm
Vaillant ecoTEC 831plus and VRC430f weather compensator 14 180 Fri Dec 23, 2011 8:48 pm
vaillant weather compensator 8 880 Mon Apr 02, 2012 1:34 pm
Central Heating Set up with Weather Compensator 12 1920 Sat Feb 07, 2009 3:15 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.