Central Heating Problems - Honeywell ST699 & V4073 Valve


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
simacc

from United Kingdom

Joined: 26 Nov 2008
Posts: 6
Location: London,
United Kingdom

PostPosted: Wed Nov 26, 2008 9:04 pm Reply with quote

I am having problems with my central heating and having a go myself to fix it. The main parts are as per the subject a Honeywell ST699 timer and a V4073 Mid Position Valve.

My partner and I have been living at the property for 11 months now and about a month ago we kept on getting caught out in the morning with no hot water. Everything was fine before and we could time the heating and the hot water separately.

Now the water doesn't heat properly and the heating doest seem to respond to whats going on with the thermostat. We also noticed that the timer was not switching on and off and was sometimes not switching off when it should have. The hot water was also coming on when the heating was and vice versa (I think!). I got my multimeter out and checked that the correct voltages were being swtiched to the valve and it didnt looked like it was. From my memory the heating wire to the valve was going from 0-150V and the hot water was not doing anything.

I thought this may be due to the timer not doing its job properly so got another one from ebay and fitted it thinking it would solve all the problems. Unfortunately it doesnt look like it has. I have just tested the heating with the thermostat turned right down and the radiators are red hot. I have also noticed that it sounds like the boiler and pump switch on as soon as I plug in the timer, is this right? One test I was going to do was to see if the valve was moving manually. With the old timer it looked like the mechanism on the valve was moving where as with the new one it doesnt.

I hope I have provided enough information for someone to be able to help (and not bored you too much!!). I cant see that there is a wiring problem as it was working in the past, which is why I was pointed towards the timer. Now I have ruled it out (I think), I'm now thinking its the valve.

Any help would be greatly appreciated.

Si

EDIT: I have just noticed the boiler and pump being active it due to the cylinder thermostat. If I turn it down then everything shuts down, as soon as you hear a click when turning it up (meaning its reached the current temp) then it all kicks off again. This is without the heating or hot water being switched on.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
gas4you

from United Kingdom

Joined: 23 Feb 2007
Posts: 17606
Location: Norfolk,
United Kingdom
Thanked: 747 times

PostPosted: Wed Nov 26, 2008 10:46 pm Reply with quote

Sorry too long a post for my attention span icon_redface.gif but I would suggest it is the 3 port valve head that is faulty.
Back to top
 Alert Moderators
Slugbabydotcom

from United Kingdom

Joined: 10 Mar 2005
Posts: 3505
Location: Middlesbrough,
United Kingdom
Thanked: 83 times

PostPosted: Wed Nov 26, 2008 10:59 pm Reply with quote

When you swapped programmers did you swap like for like? ST699 for ST699?
Did you replace the backplate and mix the wires up ?
Only 150v suggests dodgy wiring, a bad connection or dodgy relay in your programmer.
Back to top
 Alert Moderators
simacc

from United Kingdom

Joined: 26 Nov 2008
Posts: 6
Location: London,
United Kingdom

PostPosted: Thu Nov 27, 2008 8:08 am Reply with quote

Slugbabydotcom wrote:
When you swapped programmers did you swap like for like? ST699 for ST699?
Did you replace the backplate and mix the wires up ?
Only 150v suggests dodgy wiring, a bad connection or dodgy relay in your programmer.


Thanks for your reply. Yes I have swapped like for like. I have noticed that the incoming live from the fused spur is only 150V, which is a bit strange. I was doing some more tests yesterday evening and the valve looks like its turning both ways and to the centre when both are switched on.

I did, however, notice that when the valve was turning anti-clockwise the mechanism was rubbing against the lever that sets the valve to 'auto' or 'manual' and in most cases would rub so much it would knock the lever into 'manual' mode. I set both the heating and hot water to come on this morning and it all worked fine!

This now begs the question, is the ST699 I bought off ebay faulty?!
Back to top
 Alert Moderators
gas4you

from United Kingdom

Joined: 23 Feb 2007
Posts: 17606
Location: Norfolk,
United Kingdom
Thanked: 747 times

PostPosted: Thu Nov 27, 2008 8:49 am Reply with quote

Personally I think everyone who buy's off ebay needs their head testing icon_lol.gif

The grief caused just to save a few pounds never ceases to amaze me icon_eek.gif

You need to check to see if you have 240VAC going into the fused spur first then logically trace this into the heating circuit.
Back to top
 Alert Moderators
simacc

from United Kingdom

Joined: 26 Nov 2008
Posts: 6
Location: London,
United Kingdom

PostPosted: Thu Nov 27, 2008 9:05 am Reply with quote

gas4you wrote:
Personally I think everyone who buy's off ebay needs their head testing icon_lol.gif

The grief caused just to save a few pounds never ceases to amaze me icon_eek.gif

You need to check to see if you have 240VAC going into the fused spur first then logically trace this into the heating circuit.


It was a bit more than a few quid, I got it for 23 so saved about 50!

I'm going to borrow another multimeter to make sure its not the equipment measuring the voltage incorrectly too.
Back to top
 Alert Moderators
gas4you

from United Kingdom

Joined: 23 Feb 2007
Posts: 17606
Location: Norfolk,
United Kingdom
Thanked: 747 times

PostPosted: Thu Nov 27, 2008 9:10 am Reply with quote

What people tend to ignore is the fact that, in your case, it was 23 for a reason, at best second hand or nicked, at worst faulty.
Back to top
 Alert Moderators
simacc

from United Kingdom

Joined: 26 Nov 2008
Posts: 6
Location: London,
United Kingdom

PostPosted: Thu Nov 27, 2008 9:44 am Reply with quote

gas4you wrote:
What people tend to ignore is the fact that, in your case, it was 23 for a reason, at best second hand or nicked, at worst faulty.


true. looks like the later in my case.... icon_sad.gif
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8674
Location: Sussex,
United Kingdom
Thanked: 997 times

PostPosted: Thu Nov 27, 2008 11:43 am Reply with quote

simacc wrote:
I have noticed that the incoming live from the fused spur is only 150V, which is a bit strange.

That's one heck of a voltage drop!
  1. Unplug the ST699.
  2. Measure the voltage at the fused spur.
  3. Measure the voltage between terminals 1(Live) and 2(Neutral) of the backplate.
  4. If you are not getting 240v in both cases, check the tightness of all connections. If this does not give you 240v, you need to get your wiring checked from the fuse board/consumer unit.


If you do get 240v, test the ST699
  1. Check that you have a wire connecting ST699 terminal 1 to terminals 5 and 8.
  2. Trace the wire from ST699 terminal 3 (CH ON) to a terminal in the wiring centre and disconnect all other wires on that terminal.
  3. Replace the ST699, turn power on and turn CH ON and continuous at the ST699.
  4. Measure voltage at the terminal in the wiring centre. It should be 240v. If it is, the CH ON terminal of the ST699 is basically OK, but check it with the CH on the various options (timed etc) to make sure it is not a timer fault.
  5. Reconnect the wires.
  6. Trace the wire from ST699 terminal 6 (HW ON) and disconnect any other wire. Measure voltage on that terminal with HW ON, as above. This will check the HW ON side of the ST699.
  7. Reconnect the wires
  8. Trace the wire from ST699 terminal 7 (HW OFF) and disconnect any wires found. Measure the voltage on the terminal when HW is turned OFF. Should be 240v. Check it gives the same result when turned off by timer or manually.
  9. Reconnect the wires.


If everything checks out, your ST699 is OK and the fault lies somewhere else.
Back to top
 Alert Moderators
simacc

from United Kingdom

Joined: 26 Nov 2008
Posts: 6
Location: London,
United Kingdom

PostPosted: Thu Nov 27, 2008 11:56 am Reply with quote

Wow, thanks for the reply, really really useful. The main problem I was having was finding where the problem lies in the system, as Im not an expert I was having trouble fault finding. Now I can atleast find out whether the ST699 is faultly (both new and old).

Love this forum!
icon_biggrin.gif
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8674
Location: Sussex,
United Kingdom
Thanked: 997 times

PostPosted: Thu Nov 27, 2008 12:03 pm Reply with quote

You will find Honeywell Wiring Guide very helpful as it has fault finding tips for the Y-plan, which you have.
Back to top
 Alert Moderators
Slugbabydotcom

from United Kingdom

Joined: 10 Mar 2005
Posts: 3505
Location: Middlesbrough,
United Kingdom
Thanked: 83 times

PostPosted: Thu Nov 27, 2008 10:50 pm Reply with quote

The diverter probably wont funtion with only 150V going through it. Are you running the system through an extension cable or something?
Whatever , sort the voltage out before you go any further.
Long cable runs and coiled wires cause resistance which reduces voltage.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Honeywell V4073 valve 3 60 Sun Oct 14, 2012 7:02 pm
Buzzing Honeywell V4073 mid position valve 2 1140 Fri Oct 24, 2008 9:19 pm
Honeywell V4073 Mid-Position Valve - any experts? 9 1940 Wed Apr 18, 2007 8:06 pm
Honeywell V4073 midpoint valve 6 120 Wed Oct 17, 2012 12:33 pm
faulty honeywell valve V4073? 3 180 Tue Oct 26, 2010 3:59 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.