PostPosted: Tue Nov 16, 2004 3:44 pm    Post Subject:
spur length
Reply with quote Thanks

I'm trying to find out if there is a maximum distance you can install a spur socket from it's 'donor' ring main socket. Any ideas?
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
brown-nought

from United Kingdom

Joined: 02 Jul 2004
Posts: 211
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Nov 16, 2004 4:11 pm    Post Subject:
Reply with quote Thanks

How long do you want?

There are 2 limiting factors:-

1) Volt drop across the cables. You are allowed 4% from the point of origin. (at 230V thats 9V)
2) The fault loop impedance must be low enough for the circuit protection to operate within 0.4s for TN instalations

Its hard to arrive at an exact figure without knowing more about your requirments.

A basic guide however would be:-

A straight 2.5mm cable from the CU would be limited to about 16-20m for a double socket at 26A. Allowing for 10m effectively used in the ring (100m^2 -> 40m cable /4) I'd say that leaves 5-10 meters for the spur. Id say anything over 4m however needs a real calculation done. You can increase the length by using a larger spur cable.

These figures take no enviromental, instalation method or grouping factors into account so are not absolutes just guestimates.
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Tue Nov 16, 2004 6:15 pm    Post Subject:
Reply with quote Thanks

brown-nought wrote:

A straight 2.5mm cable from the CU would be limited to about 16-20m for a double socket at 26A.


you run a double socket at 26A for any significant time and you will cook it

plus you can't just add the length of the spur to your "effective" length of the ring because a ring is a 32A cuircuit
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Tue Nov 16, 2004 6:33 pm    Post Subject:
Reply with quote Thanks

brown-nought wrote:
100m^2 -> 40m cable

Where did you get that figure?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Tue Nov 16, 2004 9:12 pm    Post Subject:
Reply with quote Thanks

well it would be if the area was absoloutely square and the CU was on one side of it and everything was level and all cables run horizontally

having said that most rings don't serve anywhere near 100 square meters of floor area
Back to top
 Alert Moderators
brown-nought

from United Kingdom

Joined: 02 Jul 2004
Posts: 211
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Nov 17, 2004 11:48 am    Post Subject:
Reply with quote Thanks

Yep 40m came from a max size perfectly square ring - which must be the shortest length a maximum area ring can be.

I agree 26A isn't good for a twin socket, but it is the theoretical max that it could draw - and hence gives a Vd figure. The ring Vd calculation would need to assume 32A if protected by a 32Mcb.

As I said the figures were a guestimate.

The easiest way to get a real value for the length would be to measure the rings approx length using its ring conductor resistance value. Then calculate the Vd in the ring using 1/2 the length. From the point of spuring measure the ring Zs (or use the rings max Zs value.) Then calculate the max spur possible which still achieves 0.4s and under a 4% drop.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Wed Nov 17, 2004 12:32 pm    Post Subject:
Reply with quote Thanks

brown-nought wrote:
Yep 40m came from a max size perfectly square ring - which must be the shortest length a maximum area ring can be.

No - the shortest is 35.45m.

Quote:
I agree 26A isn't good for a twin socket, but it is the theoretical max that it could draw - and hence gives a Vd figure.

You'd better hope for terrible VD then - might keep the current down to a level where your socket does not catch fire...

Quote:
The easiest way to get a real value for the length would be to measure the rings approx length using its ring conductor resistance value. Then calculate the Vd in the ring using 1/2 the length. From the point of spuring measure the ring Zs (or use the rings max Zs value.) Then calculate the max spur possible which still achieves 0.4s and under a 4% drop.

Splendid plan, but try using ¼ of the ring length, not ½....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
brown-nought

from United Kingdom

Joined: 02 Jul 2004
Posts: 211
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Nov 17, 2004 3:07 pm    Post Subject:
Reply with quote Thanks

ban-all-sheds wrote:
No - the shortest is 35.45m.

- Of course a circle is less

ban-all-sheds wrote:
Splendid plan, but try using ¼ of the ring length, not ½....


Yes you are right I forgot that the current is split, the max value will be based on quarter the ring length. The value will become less as you move towards one end of the ring.

At the middle each leg will carry ½ the current ½ the length. Thus Vd will be L/2 * I /2.
Back to top
 Alert Moderators
Damocles

from United Kingdom

Joined: 14 Sep 2004
Posts: 1291
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Nov 18, 2004 2:25 am    Post Subject:
Reply with quote Thanks

Totally pointless talking about voltage drop limiting spur length. No one is reasonably going to install a spur on the assumption it will be required to provide so much current as you suggest. Voltage drop is based upon design current, not maximum possible current.

Difficult to decide what the actual design current might be, but on the assumption that any 13A socket, double or single, is rated at 13A, then this might be a rather better number. Or assume that average curent per socket when in use is maybe 5A?

__________________
His vorpal blade went snicker-snack
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu Nov 18, 2004 8:53 am    Post Subject:
Reply with quote Thanks

You might find that disconnection time becomes the limiting factor.

Howie - is this a hypothetical Q, or do you actually need to install a long spur?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
brown-nought

from United Kingdom

Joined: 02 Jul 2004
Posts: 211
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Nov 18, 2004 11:18 am    Post Subject:
Reply with quote Thanks

Damocles wrote:
Totally pointless talking about voltage drop limiting spur length. No one is reasonably going to install a spur on the assumption it will be required to provide so much current as you suggest.

Respectfully, I know its unlikely, but home owners should be consider electrically unskilled operatives and who knows what a spur will be used for in the future. I'm sure none of us would install a spur socket intended to supply a 26A load but there is nothing physically to stop someone later trying to use it that way. I'm not even suggesting they are drawing a constant 26A it could be a short term load.

How did I decide what figure to use? Volt drop should be calculated from the load not the rating current. So what is the load current of a twin 13A Socket? Using the maximum demand tables this says it should be the rated current of the socket - here 2x13. Thats why I used 26A. I cannot see what other figure I should use without getting into grey diversity allowances.

If you can find other regs or guidelines that say I could do something else I'm happy to be corrected and informed. However I'd say if I used 26A nobody could later come back and say I had under allowed.

The simplest solution to use a lower figure would be to spur from the load side of an FCU. That would double the V.d. limit distance.

Anyway this is getting a bit academic without knowing what howie was planning.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu Nov 18, 2004 12:09 pm    Post Subject:
Reply with quote Thanks

brown-nought wrote:
So what is the load current of a twin 13A Socket? Using the maximum demand tables this says it should be the rated current of the socket - here 2x13.

No - the rated current of a socket outlet, single, double, triple, whatever, is 13A, not n x 13A.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Damocles

from United Kingdom

Joined: 14 Sep 2004
Posts: 1291
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Nov 18, 2004 1:05 pm    Post Subject:
Reply with quote Thanks

I think the important limit is that of keeping the cable resistance low enough to ensure disconnection times are met. This is a safety issue. If voltage drop occures, that might conceivably be a safety issue but is much more likely only to be a nuisance issue.

The regulation sensibly states that a circuit should be designed to provide the current demanded, not over-engineered for something extra. This might mean that you are planning to add a spur which you know is only going to be used for a radio and table lamp. Yes, someone may come along in the future and use a heater. But the necessary thing is to ensure the system is safe. If you need to cheat a bit and assume 10A maximum current to stretch the voltage drop cable length a little, then I think that would be considered acceptable if it makes the installation doable. It is not against the spirit of the regulations.

Would you concede the quite likely scenario that it is possible to wire a house with just one 32A socket ring, and that it is also quite likely that this would never trip. I feel it is much better practice if considering the installation as a whole to split the sockets into up/down/kitch as appropriate for reasons of discrimination rather than total load. This means the rings are very likely to be under-loaded. This makes assuming a low overall demand more reasonable.

I am not saying anyone should ignore voltage drop. But I think it is better to keep advice simple as much as possible. The important thing is disconnection time. Anyone reading advice here should get that point before starting to worry about voltage drop.

Which unfortunately has still not answered the original post. The actual answer is that it would depend upon the existing length of the ring and at what point you spurred off. Advice has to be. keep it short.

__________________
His vorpal blade went snicker-snack
Back to top
 Alert Moderators
brown-nought

from United Kingdom

Joined: 02 Jul 2004
Posts: 211
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Nov 18, 2004 1:31 pm    Post Subject:
Reply with quote Thanks

Guys,

I'll shut up about V.d. after this - promise! - Agreed disconnection is more important from a safety perspective.

B-a-s are you sure about 13A for doubles?? (Trips are always limited by a 13a fuse and singles by design but MK specs rate their doubles at 13a per outlet. i.e. 26a)

I've racked my brains to justify V.d. concerns and the only case that comes to mind might be under volted fan heaters getting too hot!

At the end of the day I'm a pragmatist too and would try hard to make the calculation fit the result needed. (but we ain't got one howie!!)

Damocles Do you really fit more than one ring?? I've always seen it as an energy saving feature. icon_lol.gif
Back to top
 Alert Moderators
Damocles

from United Kingdom

Joined: 14 Sep 2004
Posts: 1291
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Nov 18, 2004 1:48 pm    Post Subject:
Reply with quote Thanks

Well sadly it depends whose paying. Yes, hard to say exactly how much electricity might be saved by reducing voltage drop, which just means power wasted heating cables. But probably a power station or two by good design. Has to be balanced against the cost of that extra copper. More rings likely means they are each shorter.

__________________
His vorpal blade went snicker-snack
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Spur Length ?? 10 680 Sun Oct 22, 2006 11:00 am
cable length for spur from ring 9 460 Sun Jun 22, 2008 7:29 pm
Spur cable length 11 1600 Wed Oct 20, 2004 1:53 pm
Cable length for a ring main spur ? 7 960 Thu Aug 26, 2004 8:33 am
Length of Spur! 3 360 Mon Apr 10, 2006 9:18 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.