Rcd do not trip at x1


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
Joe100w

from United Kingdom

Joined: 04 Apr 2009
Posts: 30
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Apr 06, 2009 2:22 pm    Post Subject:
Rcd do not trip at x1
Reply with quote Thanks

hi,

I am testing a circuit that goes to the garden with armoured cable. The RCD will not trip at x 1 (gets over 400ms) but trips fine on x5. The other circuits seems to be fine with the RCD test (30 mA). Using megger mft 1552. Any reason?

When I move that circuit to the other RCD (30 mA) it trips fine within the time.

My puzzle why will the garden circuit not trip at x 1. What could have been wrong.

Thanks.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
ColJack

from United Kingdom

Joined: 16 Feb 2007
Posts: 7599
Location: West Midlands,
United Kingdom
Thanked: 129 times

PostPosted: Mon Apr 06, 2009 2:31 pm    Post Subject:
Reply with quote Thanks

distance of run? dodgy earth? dodgy neutral?

what are the Zs readings for the garden circuit?
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16480
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Mon Apr 06, 2009 4:06 pm    Post Subject:
Reply with quote Thanks

It is incorrect to test an RCD from a final circuit.

Test it in isolation.


What was the Zs at that point before you started work?

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
Joe100w

from United Kingdom

Joined: 04 Apr 2009
Posts: 30
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Apr 06, 2009 4:27 pm    Post Subject:
Reply with quote Thanks

Zs is 1.32, Protected by type B MCB rated at 16A. Wiring all 3 is 2.5 mm and the armoured also is connected to Earth.

Insulation resistance >299 on all three.

Could not get a trip on 1 RCD with several attemps, but same circuit was fine when swapped over to the other RCD
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16480
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Mon Apr 06, 2009 4:32 pm    Post Subject:
Reply with quote Thanks

Test the RCD in isolation. If it fails, swap it out.

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
Joe100w

from United Kingdom

Joined: 04 Apr 2009
Posts: 30
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Apr 06, 2009 5:15 pm    Post Subject:
Reply with quote Thanks

Securespart

Might sound silly, how do I test Rcd in isolation.
icon_rolleyes.gif
Back to top
 Alert Moderators
ColJack

from United Kingdom

Joined: 16 Feb 2007
Posts: 7599
Location: West Midlands,
United Kingdom
Thanked: 129 times

PostPosted: Mon Apr 06, 2009 5:26 pm    Post Subject:
Reply with quote Thanks

take the cables out of it and put the test leads on the load side of it...
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16480
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Mon Apr 06, 2009 10:43 pm    Post Subject:
Reply with quote Thanks

Or if it is difficult to take the cables out of the outgoing terminals, switch off all the MCB's attached to that RCD to isolate the live terminal, then either disconnect all the neutrals from the busbar attached to that RCD or pull out (if it is flexible) the neutral feed to that busbar.

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
RCD trips on 'no trip test' 6 400 Thu May 15, 2008 6:20 am
lights gone out but trip switch still on 7 1240 Mon Mar 31, 2008 8:00 pm
Electric Shower Trip 6 260 Fri Mar 28, 2008 9:03 am
why does the RCD trip the moment I plug something in? 3 260 Wed May 28, 2008 4:45 pm
Outdoor RCD socket Trip 7 220 Mon Jun 23, 2008 10:30 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.