Strange boiler problem...


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
  View previous topic :: View next topic  
Author Message
ellal

from United Kingdom

Joined: 23 May 2004
Posts: 984
Location: United Kingdom
Thanked: 1 time

PostPosted: Tue Aug 11, 2009 7:32 am    Post Subject:
Strange boiler problem...
Reply with quote Thanks

Despite having the boiler set to hot water only, yesterday some of the radiators came on.

The roomstat has no effect, although the relay switches over.

The timer (on the boiler) was in timed position, and turning it to off turned the heating off. However, putting it back to timed (with boiler still set to hot water only) led to some radiators coming back on again, regardless of whether it was in an on or off period.

The radiators that come on are dotted around the house, but bore no relation as to the TRV settings.

Boiler is a Halstead Ace High. (Had a problem a while back which required a diaphragm change). Pressure is unchanged at 1.5bar.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Steve69the69Gas

from United Kingdom

Joined: 02 Aug 2008
Posts: 416
Location: Nottinghamshire,
United Kingdom
Thanked: 8 times

PostPosted: Tue Aug 11, 2009 7:43 am    Post Subject:
Reply with quote Thanks

Diverter again?
Back to top
 Alert Moderators
ellal

from United Kingdom

Joined: 23 May 2004
Posts: 984
Location: United Kingdom
Thanked: 1 time

PostPosted: Tue Aug 11, 2009 7:54 am    Post Subject:
Reply with quote Thanks

when it went before it affected the hot water, and kept switching on/off.

could the same diaphram give a different problem?
Back to top
 Alert Moderators
Boilerman2

from United Kingdom

Joined: 10 Jun 2009
Posts: 575
Location: Suffolk,
United Kingdom
Thanked: 53 times

PostPosted: Tue Aug 11, 2009 7:48 pm    Post Subject:
Reply with quote Thanks

The Diaphragm only interacts with the Diverer Valve, they are two separate parts attached, sounds like the diverter valve is letting by possibly full of system crap, (thats techy talk for debris)

Diverer valve can be brought separatetly from the Diaphragm chamber icon_wink.gif
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Problem with Falcon II Combi boiler (no CH, strange noises) 7 1400 Tue Jan 16, 2007 5:17 pm
Potterton Lynx Boiler problem.. slightly strange. 8 620 Thu May 10, 2007 6:58 am
Combi boiler strange pressure rising problem 10 580 Fri Feb 16, 2007 10:42 pm
Strange problem with radiators...? 4 480 Thu Dec 14, 2006 9:35 pm
Strange Problem 2 260 Sun Jan 28, 2007 11:27 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.