I had a problem with a SIME Super 90 plus Boiler.
The symptoms were that when I had a shower, the boiler didn't start up unless I ran the hot tap at the same time. By talking it through with a friendly plumber we diagnosed that this was probably the diaphragm inside the Diverter Valve. This is a rubber diaphragm which when it has more water pressure on one side, moves a metal rod up which pushes the microswitch on which starts the boiler. (When I removed the old diaphragm, the rubber was corroded with a hole in it which explains why it wasn't working correctly.)
I was quoted by a couple of plumbers about £200 to replace the diverter valve so decided to have a go myself.
The process of changing the diaphragm was relatively straightforward - it took about 90 minutes.
(1) Order a new diaphragm:
I contacted MJT Controls (In Bristol UK):
www.mjtcontrols.co.uk
They asked me for the Ref No for the boiler which was inside the front cover of the boiler which is a number which begins with 808 or 809 and four more digits. They can use this to check that you're ordeing the right part no.
The part no for a diverter valve with them is: 6102801
which is about £70
BUT I asked for just the diaphragm which was just £6 !! Delivered a couple of days later.
(2) Preparation
Remove front of boiler
Turn off mains water.
Relieve water pressure by turning on cold and hot taps in a sink.
Disconnect electric power to boiler (I did it by removing fuse)
(3) Remove Diverter valve.
It's a bit awkward as it's at the back right - a brass coloured unit with five pipes connecting and a black plastic unit fixed to top which is the microswitch. It's a matter of undoing the five nuts and then removing the three electric connections to the microswitch (keep a record on paper of the order)
(4) Change diaphragm.
Undo about 8 screw in diverter valve and open it up.
A large spring pushes the two parts apart. Remember which way these go so you can put it back together. My diaphragm had a hole in it.
Put new diaphragm in and push big spring down and put 8 screws back in.
(Note that the two side pipes go out opposite each other.
(5) Replace Diverter valve.
Revers of (3) - can be a bit fiddly.
(6) Finishing
Turn on water
Bring pressure back up by truning a tap underneath boiler so that pressure of boiler comes up to red mark ont he dial.
Run hot tap until flowing fully.
Put fuse back in to bring power back on.
(7) Have a nice hot shower!
Sit back and have a beer
Thanks for this thread - it made it possible for me to save about £160 !
Regards
Suhada