Not exactly DIY guys but something ive come across and would appreciatte some comments from anyone who has experience of such circuits. Been reading posts on the net and other forums regarding the subjetct.
The situation i have encountered (which im on with doing some planning for) involves a 3phase lighting circuit wired as follows,
A 32A TP mcb supplying a submain mini CU. The mini CU houses 3 x single pole 20A mcb's each supplied by a phase from the 32A breaker. A 4 core swa cable runs from this mini CU up into the roof to supply light fittings. Each phase of the swa is connected to one of the 20A mcbs and each phase supplies 6 400W SON fittings. The other core of the swa is used as the neutral which is a shared neutral between the 3 phases.
As far as i understand from 7671 this circuit complies (dont have my copy on me so i cant refer any regs at minute)
Now several points seem to be raised in previous internet posts about the compliance of this setup. These are as follows
1, The OPD protecting the 'circuit' needs to be linked i.e a TP MCB.In this instance the circuit has a TP isolation device,but it has further downstream SP devices (I.E the 20A devices). Anyone see a problem?
2, Previous posts on this topic seem to mistake this shared neutral as a borrowed neutral which are two different things imo.
3, The balancing of the phases. With all SP devices switched on then the loads should be balanced so fine. Even with one switch turned off the Neutral conductor is still adequetlly sized to carry the imbalance as far as i can see it.
4, Loss of neutral on circuit. Whats the worst effect this could have on the light fittings. Nothing too detremental as far as i can see.
Apologies for the long post but its not a circuit setup im used to and am keen to educate myself about it.
Regards.
The situation i have encountered (which im on with doing some planning for) involves a 3phase lighting circuit wired as follows,
A 32A TP mcb supplying a submain mini CU. The mini CU houses 3 x single pole 20A mcb's each supplied by a phase from the 32A breaker. A 4 core swa cable runs from this mini CU up into the roof to supply light fittings. Each phase of the swa is connected to one of the 20A mcbs and each phase supplies 6 400W SON fittings. The other core of the swa is used as the neutral which is a shared neutral between the 3 phases.
As far as i understand from 7671 this circuit complies (dont have my copy on me so i cant refer any regs at minute)
Now several points seem to be raised in previous internet posts about the compliance of this setup. These are as follows
1, The OPD protecting the 'circuit' needs to be linked i.e a TP MCB.In this instance the circuit has a TP isolation device,but it has further downstream SP devices (I.E the 20A devices). Anyone see a problem?
2, Previous posts on this topic seem to mistake this shared neutral as a borrowed neutral which are two different things imo.
3, The balancing of the phases. With all SP devices switched on then the loads should be balanced so fine. Even with one switch turned off the Neutral conductor is still adequetlly sized to carry the imbalance as far as i can see it.
4, Loss of neutral on circuit. Whats the worst effect this could have on the light fittings. Nothing too detremental as far as i can see.
Apologies for the long post but its not a circuit setup im used to and am keen to educate myself about it.
Regards.