DIYnot
Local | Network
   DIYnot > Forums
Local | Network
PFC on a TT system
Author Message
too old to learn
from United Kingdom
PostPosted: Tue Oct 13, 2009 2:24 pm Reply with quote
I have been round my friends house as he has a TT system and I have never worked on these installations before. (yeah yeah, pathetic I am! lol)
Whilst doing the PFC the result was 11 Amps.
Is this correct for a TT system?
I am guessing it is as the Ze was 20.9 ohms.
I was just expecting similar readings to a TNS system where it is above 1KA.
Guess this is the reason TT supplys (I know all do now to the 17th) needed time delayed RCD's to the 16th edition
Back to top
 Alert Moderators
toasty
from United Kingdom
Thanked: 5 times
PostPosted: Tue Oct 13, 2009 2:37 pm Reply with quote
I don't understand the question.
If the Ze is 20.9ohms, and the supply voltage is 230v, then surely the max fault current to earth can't be greater than about 11amps (230/20.9)
With TNS systems, the earth impedance is much much much lower, so of course the fault current to earth is a lot higher.
Is that what you mean? Sorry, but assuming you are a sparky, I would have thought it obvious.
Dan
Back to top
 Alert Moderators
Taylortwocities
from United Kingdom
Thanked: 1095 times
PostPosted: Tue Oct 13, 2009 3:26 pm Reply with quote
The figure you put in the Schedule of Tests, and the one you need to determine, will be the higher of PSC (Prospective Short Circuit Current ) and PFC.
In TT the PFC will not be very high as you it is always limited by the mass of earth.
Back to top
 Alert Moderators
too old to learn
from United Kingdom
Yes I know that!
My thoughts are that if there is a PEFC or PSFC then there is only 11A runnign down the live. This is therefore not enough to trip a ring breaker.
Therefore the need for RCD's.
Main point is that I have never done a TT suppply and I am using his house as practice. was just surprised at first to see such a low reading comapred to TNS system.
So i guess this value is correct.
Therefore I can Write this down as the PFC on the test sheet
thanks
Back to top
 Alert Moderators
Taylortwocities
from United Kingdom
Thanked: 1095 times
PostPosted: Tue Oct 13, 2009 3:29 pm Reply with quote
too old to learn wrote:
Yes I know that!
Back to top
 Alert Moderators
too old to learn
from United Kingdom
PostPosted: Tue Oct 13, 2009 3:33 pm Reply with quote
sorry Taylorwocities, you got there just before me.
Least i know for future reference that thsi is what i wirte in.
Back to top
 Alert Moderators
Spark123
from United Kingdom
Thanked: 415 times
PostPosted: Tue Oct 13, 2009 4:10 pm Reply with quote
Your PFC will almost certainly be phase to neutral on a TT system (PSCC - prospective short circuit current).
The PEFC (prospective earth fault current) will be low - in your case 11A. PFC (prospective fault current) is the greatest fault current which can flow in an installation i.e. the PSCC or PEFC, which ever is greater.
If there was a PSCC of 11A then your lights would be very dim!
Same as on any TN-S, TN-CS, single or 3 phase system it is the max fault current which can flow - to make sure your fuses/MCBs are up to the job (or backed up).
Back to top
 Alert Moderators
too old to learn
from United Kingdom
PostPosted: Tue Oct 13, 2009 7:27 pm Reply with quote
well i have been and measured the PSFC (betwenn live and neutral) and the result was 1.18KV. this is the answer that I was first expecting and therefore why i asked the first question.
Thereofre this is the value that I would put down on my test form.
One question I have now? how come if my PSCC was 11A my ligths would be like my brain, very dim icon_smile.gif ha ha
Back to top
 Alert Moderators
londonboy
from United Kingdom
Thanked: 149 times
PostPosted: Tue Oct 13, 2009 7:31 pm Reply with quote
I may be wrong but don't you put worst case figures down?
ie,
lowest for IR
lowest for pfc
highest for zs
Back to top
 Alert Moderators
RF Lighting
from United Kingdom
Thanked: 1022 times
PostPosted: Tue Oct 13, 2009 7:43 pm Reply with quote
You put the highest for Ipfc
That is the worst case scenario - i.e. the higher the fault current, the more damage could be done to the installation, such as melted circuit breakers etc.
Back to top
 Alert Moderators
londonboy
from United Kingdom
Thanked: 149 times
PostPosted: Tue Oct 13, 2009 7:48 pm Reply with quote
Yeh course! I was thinking about not enough current flowing to disconnect breaker, obviously this is to do with Ze.
Back to top
 Alert Moderators
RF Lighting
from United Kingdom
Thanked: 1022 times
PostPosted: Tue Oct 13, 2009 7:51 pm Reply with quote
Back to top
 Alert Moderators
Spark123
from United Kingdom
Thanked: 415 times
PostPosted: Tue Oct 13, 2009 9:15 pm Reply with quote
Your lights would be dim as the impedance of the supply conductors (phase and neutral) would have to be very high to give you a figure as low as 11A. Think about impedances in series acting like a potential divider with your current using apparatus - the volt drop would be massive!
Back to top
 Alert Moderators
too old to learn
from United Kingdom
PostPosted: Wed Oct 14, 2009 8:10 am Reply with quote
Back to top
 Alert Moderators
Page 1 of 1
Jump to:
Wiring centre for large multi-zone wet UFH system 9 560 Mon Sep 20, 2010 9:56 pm
Replace light fixture on loop system 3 12720 Fri Oct 08, 2010 7:13 pm
earthing system(UK) 21 1760 Wed Dec 01, 2010 2:26 pm
2 fuse spurs on a heating system 28 680 Sat Dec 18, 2010 9:02 pm
Will the MK Grid Plus system work in plastic drywall bkboxs? 14 660 Wed Aug 25, 2010 9:52 pm
DIYnot
Please read our Privacy Policy. Copyright © 2000-2015 DIYnot Limited.