BAXI SOLO 2PF IGNITION PROBLEM

Joined
3 Jan 2009
Messages
4
Reaction score
0
Location
Lancashire
Country
United Kingdom
My boiler takes around 50 sparks to fire up. The spark is good and the gas is there as it smells strongly of unburned gas afterwards. This only happens when the boiler fires up first thing, restarts when warm are fine.
Any advice appreciated.
Cheers
 
Sponsored Links
Sponsored Links
Anotherbgeng is correct. If you feel competent you can unscrew it inside the combustion chamber. You can clean it with air presure or if necessary fine (ie 5 amp) fuse wire. Put the combustion chamber front back on before trying. It wont work unless the correct pressure differential is detected.
 