Gravity fed system but told i cant install a shower pump??


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
stevom2004

from United Kingdom

Joined: 23 Dec 2009
Posts: 2
Location: Bristol,
United Kingdom

PostPosted: Wed Dec 23, 2009 12:48 pm Reply with quote

Recently splashed out on a steam shower system for a christmas treat. It needs a balanced water pressure to work effectively.
I have a cold water tank in loft and hot water tank in airing cupboard and so identified my system as a gravity fed system and so bought a 3 bar twin impellar water pump to be installed. However the guy i got in to price up the job says that the cold is actually mains fed and so will not install pump. Please help, i have a feeling hes wrong as all the diagrams i look at online scream that it is a gravity fed system which m,eans it should be fine to install the pump....
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
seco services

from United Kingdom

Joined: 03 Dec 2007
Posts: 15582
Location: Essex,
United Kingdom
Thanked: 1235 times

PostPosted: Wed Dec 23, 2009 1:01 pm Reply with quote

is this the type of cylinder you have ?


with two tanks in the loft ?
what is he saying is cold mains feed ?
have you any pics ?
Back to top
 Alert Moderators
gas4you

from United Kingdom

Joined: 23 Feb 2007
Posts: 17233
Location: Norfolk,
United Kingdom
Thanked: 600 times

PostPosted: Wed Dec 23, 2009 1:09 pm Reply with quote

Sounds like he doesn't know what he is talking about icon_rolleyes.gif

The cold feed for the shower will come direct from the cold storage tank that supplys the HW cylinder, to the pump, and the HW supply from the pump should come from its own fitting on the HW cylinder, thereby giving you a fully balanced supply.

Your only possible problem could be, especially with a 3 Bar pump, that the cold storage tank is not big enough to supply enough water to keep up with the pump.

I have assumed that by 2 tanks, you mean 1 large and 1 small, which would be the heating expansion tank.

However you may have 2 large tanks in tandem. You need to clarify this first.
Back to top
 Alert Moderators
stem

from United Kingdom

Joined: 20 Jul 2005
Posts: 1621
Location: Nottinghamshire,
United Kingdom
Thanked: 231 times

PostPosted: Wed Dec 23, 2009 1:27 pm Reply with quote

stevom2004 wrote:

I have a cold water tank in loft and hot water tank in airing cupboard

What you describe is a gravity hot water supply (By "hot water tank" in the airing cupboard I am assuming you mean "hot water cylinder" as per the photo from seco services) The existing cold water supply will probably be direct from the cold water main at a higer pressure and if so it will not presently be balanced.

However a gravity cold water supply can be taken from the tank in the loft to feed the pump. Then as both hot and cold supplies come from the same tank, they would be balanced, as per the diagram below.

Back to top
 Alert Moderators
kittedup

from United Kingdom

Joined: 13 Nov 2008
Posts: 479
Location: Somerset,
United Kingdom
Thanked: 116 times

PostPosted: Wed Dec 23, 2009 1:58 pm Reply with quote

how big is the tank in the loft? You may have a combined hw cylinder which means all the cold taps will be mains fed.
Back to top
 Alert Moderators
stevom2004

from United Kingdom

Joined: 23 Dec 2009
Posts: 2
Location: Bristol,
United Kingdom

PostPosted: Wed Dec 23, 2009 3:41 pm Reply with quote


here are the photos of what is there...
Back to top
 Alert Moderators
seco services

from United Kingdom

Joined: 03 Dec 2007
Posts: 15582
Location: Essex,
United Kingdom
Thanked: 1235 times

PostPosted: Wed Dec 23, 2009 4:35 pm Reply with quote

thats a standard gravity hw cylinder
so no prblem adding a pump to the system as shown above.

fit a surrey flange or essex flange to the cylinder



and cold feed from the cws.
Back to top
 Alert Moderators
Nige F

from United Kingdom

Joined: 28 Jun 2005
Posts: 15963
Location: United Kingdom
Thanked: 780 times

PostPosted: Wed Dec 23, 2009 4:53 pm Reply with quote

and cobble a bit more wood round the storage cistern icon_eek.gif some diagonal braces of 6x1 inch timber wouldn`t go amiss
Back to top
 Alert Moderators
Jasonb

from United Kingdom

Joined: 20 Aug 2004
Posts: 2420
Location: Surrey,
United Kingdom
Thanked: 91 times

PostPosted: Wed Dec 23, 2009 4:59 pm Reply with quote

Thats quite a small tank in the loft and there is only ONE downfeed which is likely doing the hot.

So cold must be off the mains. You would need to change to a larger storage tank in the loft and take an additional cold feed to the shower from it.

Jason
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
What i've been told! 20 840 Thu May 18, 2006 12:49 pm
Power Flush, been told it can't be done! 25 2540 Fri Nov 12, 2010 6:12 pm
Boiler flue - am I being told the truth? 20 1160 Fri Oct 23, 2009 9:21 am
Pelchy told me this Yesterday ! 6 160 Sat Feb 04, 2012 11:22 pm
adding a pump to gravity hot water system 2 440 Mon Apr 19, 2010 3:42 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.