Shower install, 10.5kw on 6mm cable?


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
darchy

from United Kingdom

Joined: 01 Mar 2005
Posts: 12
Location: Gloucestershire,
United Kingdom

PostPosted: Tue Mar 01, 2005 10:41 am Reply with quote

Hi, I am about to fit a new shower into my bathroom, i have bought a 10.5 kw triton shower. There is already a shower pull cord switch in the bathroom with a 6mm cable leading to the fuse box which has a 40A RCD & 100A main switch. is this setup ok?

your opinions would be appreciated

Many thanks

Shaun
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
kai

from United Kingdom

Joined: 15 Aug 2004
Posts: 1066
Location: United Kingdom
Thanked: 39 times

PostPosted: Tue Mar 01, 2005 11:22 am Reply with quote

No - you must use a 10.0. sq.mm. cable at the very least - have you filled in the Part P Building Notice to the Local Council yet?
Back to top
 Alert Moderators
felix

from United Kingdom

Joined: 23 Jan 2005
Posts: 898
Location: United Kingdom
Thanked: 2 times

PostPosted: Tue Mar 01, 2005 1:08 pm Reply with quote

That pull cord switch might be rated at 30 amps only, in which case the contacts should burn quite nicely. A 40 amp breaker is only good for 9.6 kilowatts.
Back to top
 Alert Moderators
darchy

from United Kingdom

Joined: 01 Mar 2005
Posts: 12
Location: Gloucestershire,
United Kingdom

PostPosted: Tue Mar 01, 2005 1:45 pm Reply with quote

Great thanks for that, thats cleared up a few doubts I had in mind, I'll now return the shower & exchange for a lower rated unit. What would you guys advise is the maximum you would fit in such a specification? I'm not looking to rewire the run to suit the shower, however, if needed i would consider upgrading the RCD etc.

Cheers again

Shaun
Back to top
 Alert Moderators
darchy

from United Kingdom

Joined: 01 Mar 2005
Posts: 12
Location: Gloucestershire,
United Kingdom

PostPosted: Tue Mar 01, 2005 1:52 pm Reply with quote

I've just checked the pull switch again & it is rated 45a. Just another quicky, i'm probably wrong but I thought that it was ok to wire in/change a shower to an existing installation without notifying the council?

Shaun
Back to top
 Alert Moderators
felix

from United Kingdom

Joined: 23 Jan 2005
Posts: 898
Location: United Kingdom
Thanked: 2 times

PostPosted: Tue Mar 01, 2005 2:37 pm Reply with quote

Your 40 amp breaker is good for a 9.5 kW shower. The cable is actually rated at 51 amps in free air but only 37 amps in conduit. Where is yours? An 8.5 kW shower will leave you some spare breaker capacity and draw a fraction over 35 amps. Long, long ago I had a 7 kW shower. The flow was a bit slow in winter but it still worked and was cheaper to run. You don't have to have the biggest shower in the shop.
Back to top
 Alert Moderators
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 5776
Location: United Kingdom
Thanked: 137 times

PostPosted: Tue Mar 01, 2005 3:02 pm Reply with quote

I don't think I'd want anything over 8.5kw on 6mm (this does *not* imply that 8.5kw and below is definaly ok on 6mm, all depends on volt drop, disconnect time, specing factors, etc), and even then, 10mm would be better even then.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 24861
Location: Cheshire,
United Kingdom
Thanked: 423 times

PostPosted: Tue Mar 01, 2005 4:38 pm Reply with quote

Are we using 230V in our calcs?

40A at 230V = 9,200W.

The general feeling here is that 6mm2 is good for up to 8.5kW.

As Adam says, though, this is NOT a hard and fast rule.
Back to top
 Alert Moderators
darchy

from United Kingdom

Joined: 01 Mar 2005
Posts: 12
Location: Gloucestershire,
United Kingdom

PostPosted: Tue Mar 01, 2005 4:59 pm Reply with quote

The shower itself is rated 10.5 KW @ 240v. Deeper in the book it gives a rating of 9.6kw @ 230V, using that guide, the 8.5kw should be approx 7.8kw @ 230v, the 9.5 is 8.7 @ 230v. I feel the 8.5 @ 240 would be much better for my purposes as I can't justify having the cable replaced (cost reasons). The fuse box in my house is located in my front porch, the shower cable + all others then go up the inside wall into the attic (this is in a large uninsulated plasterboard box section) , across and into the bathroom pull switch

Cheers again to all of you for your help

Shaun
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
cable size and mcb for shower install 2 2420 Thu Mar 27, 2008 8:57 pm
Shower extraction install - ceiling or wall? -approx cost? 6 320 Wed May 12, 2010 12:30 pm
Shower Feed Install 11 2380 Wed Feb 06, 2008 2:07 pm
Fresh 9.5KW Shower Install 11 2180 Tue Mar 14, 2006 11:20 am
Shower install, old fuse box 19 2620 Mon Oct 27, 2008 9:57 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.