Ring Mains

This topic originated from the How to page called Miniature circuit breakers (MCBs)
Click here to return to the page called Miniature circuit breakers (MCBs).

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
strummer

from United Kingdom

Joined: 21 Mar 2005
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Mar 21, 2005 8:15 pm    Post Subject:
Ring Mains
Reply with quote Thanks

Am I correct in assuming that both ends of a ring main should be supplied from the same MCB. Logic tells me that this has to be so.

Am I also correct in assuming that an MCB should feed one and only one ring main ??

The installation is further complicated in that night storage heaters could have been supplied at one point. That being the case what would a blue MCB (16A) have been used for. icon_confused.gif
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Mon Mar 21, 2005 8:32 pm    Post Subject:
Re: Ring Mains
Reply with quote Thanks

strummer wrote:
Am I correct in assuming that both ends of a ring main should be supplied from the same MCB. Logic tells me that this has to be so.

Absolutely yes.

Quote:
Am I also correct in assuming that an MCB should feed one and only one ring main ??

Yes

Quote:
The installation is further complicated in that night storage heaters could have been supplied at one point. That being the case what would a blue MCB (16A) have been used for. icon_confused.gif

Night Storage Heaters?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
theshogun

from United Kingdom

Joined: 25 Feb 2005
Posts: 102
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Mar 21, 2005 8:35 pm    Post Subject:
Reply with quote Thanks

Quote:
Am I correct in assuming that both ends of a ring main should be supplied from the same MCB. Logic tells me that this has to be so.


Yes

Quote:

Am I also correct in assuming that an MCB should feed one and only one ring main ??


Yes a 32 amp MCB normally

Night storage heater are normally wired on separate circuits backed by a 16 amp MCB ,these are normally in a separate cu, to the normal house circuits cu ie, lights,sockets,cooker etc.
__________________
moderator

edited to correct quote icon_wink.gif
Back to top
 Alert Moderators
strummer

from United Kingdom

Joined: 21 Mar 2005
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Mar 21, 2005 11:06 pm    Post Subject:
Reply with quote Thanks

Thanks alot. That was exactly what I wanted to know, but I might be back.
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Tue Mar 22, 2005 9:40 am    Post Subject:
Re: Ring Mains
Reply with quote Thanks

strummer wrote:
Am I correct in assuming that both ends of a ring main should be supplied from the same MCB. Logic tells me that this has to be so.

as already said ABSOLOUTELY YES
strummer wrote:

Am I also correct in assuming that an MCB should feed one and only one ring main ??

Ideally yes but theres nothing dangerous about doubling them up it just means you are limited to 32A total acrross the two rings.

strummer wrote:

The installation is further complicated in that night storage heaters could have been supplied at one point. That being the case what would a blue MCB (16A) have been used for. icon_confused.gif

usually used for dedicated appliance cuircuits for appliances up to just over 3KW or single socket cuircuits that used to be dedicated appliance cuircuits. The appliances in question are usually those that draw power for extended periods such as fixed space heaters (both direct and storage) and immersion heaters.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Ring mains! 6 460 Sat Sep 11, 2004 9:16 am
Upgrading from radial mains to two ring main circuits 11 860 Thu Aug 25, 2005 12:24 pm
BAN THE USE OF RING MAINS OR NOT 54 1720 Thu Dec 28, 2006 8:22 am
Help - accidental drll into ring mains 24 980 Thu Dec 28, 2006 6:16 pm
Extending ring mains, cable sizes,voltage drops etc 2 500 Wed Feb 16, 2005 4:47 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.