Can anyone explain 411.3.2.3 to me please?
Ta.
Ta.
Can anyone explain 411.3.2.3 to me please?
Ta.
where are you getting your 300ms from?Question 1.
If TT disconnection times are 0.2 s, how does that reconcile with RCD's disconnecting at anything up to 0.3 s?
HI folks, recently I had to install an Earth rod at a property. The Ze reading was 13.4Ohms.
So naturally when carrying out Zs readings I expected them to be higher and not meet current maximum values.
This is the only time I have come across a TT at work and am struggling to see how to reconcile these values, the property is going to be fully refurbed soon
I remember Securespark? on about compiling a TT readings guide quite a while ago
If you can't meet the max Zs value for an MCB/fuse then you need to use RCD protection for all connected circuits and the respective RCD max Zs figures, with a Ze of 13.4 ohms these are easy peasy to meet, for example if you have a max touch voltage of 50v and are using a 30mA RCD then the max theoretical Zs for the circuit is 50/0.03 = 1666 ohms, although in reality if you measured anything like that you'd be looking for a problem!So naturally when carrying out Zs readings I expected them to be higher and not meet current maximum values.
This is the only time I have come across a TT at work and am struggling to see how to reconcile these values, the property is going to be fully refurbed soon
If you still read it as 2x then a time delayed RCD will disconnect within 200mS as required by 411.3.3.2.