Hello everyone.
I've just been called back to a panel i fitted over 15 years ago.
Replaced the battery and did a full reset with new user codes (new owner just moved in)
The entry circuit refuses to accept the delay time and triggers the alarm as soon as the door is opened.

I've set zone one as entry (6) and chime (7) and the delay time at 20secs.

Anyone got any clues?

Cheers in advance.

Gary
 
Sponsored Links
Wrong, oopsa.

Set the zone as Enrty/Exit not Entry Route.
Problem solved.
 
Enrty zone is 6.

Final Exit is 5.

The issue here is the entry zone is triggering as it does not see the Final Exit zone open.

Trust me.
 
Sponsored Links
Enrty zone is 6.

Final Exit is 5.

The issue here is the entry zone is triggering as it does not see the Final Exit zone open.

Trust me.

Cheers Alarm, but there's nothing in my info to set as Ent/Ex?
All i got is this;

x = Zone type, one of:
0 = nu (not used) y
1 = PA (panic alarm)
2 = Fr (fire zone)
3 = Al (normal alarm)
4 = 24 (24 hour zone)
5 = FE (final exit)
6 = ER (entry route)
y = Zone attributes, any of:
7 = ch (chime)
8 = St (soak test)
9 = 2A (double knock)
B = b (armed in part set B)
C = c (armed in part set C)
OMIT = OA (omit allow)
 
I told you Entry Exit option 5.

Final exit if you must, option 5.

Final exit as in last door to close.................make any sence?
 