Radial to Ring

This topic originated from the How to page called Converting a radial circuit to ring circuits
Click here to return to the page called Converting a radial circuit to ring circuits.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
BJC

from United Kingdom

Joined: 23 May 2005
Posts: 40
Location: Edinburgh,
United Kingdom
Thanked: 0 times

PostPosted: Mon May 23, 2005 6:58 am    Post Subject:
Radial to Ring
Reply with quote Thanks

I have a cooker circuit in 10mm T&E which is no longer required. Is it safe/lawful to create a ring at the end of this in 2.5 T&E and simply change the MCB in the consumer unit to 30A i.e. use the 10mm T&E as an extension of the CU. Otherwise I'll need to run two new 2.5 T&E cables.

Regards

Brian
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
pna

from United Kingdom

Joined: 26 Aug 2004
Posts: 156
Location: Cambridgeshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon May 23, 2005 3:18 pm    Post Subject:
Reply with quote Thanks

Yes - no problem in having part of the circuit in higher spec cable than is necessary.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Mon May 23, 2005 4:09 pm    Post Subject:
Reply with quote Thanks

It's neither unsafe, nor unlawful.

BUT -

It is different, and electricians don't like different.

It makes testing more difficult, as the ring continuity etc tests can't be done at the CU.

There is always a chance that some future occupant will see a 10mm² cooker cable and but the MCB back up to 45A....

Try very hard not to do it like this.....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
BJC

from United Kingdom

Joined: 23 May 2005
Posts: 40
Location: Edinburgh,
United Kingdom
Thanked: 0 times

PostPosted: Mon May 23, 2005 7:16 pm    Post Subject:
Reply with quote Thanks

Thanks chaps. Hadn't thought about future occupants misinterpreting my handywork. Will probably put in a new ring from the CU and retain the cooker circuit for a new fan oven I'm installing.
Back to top
 Alert Moderators
Big_Spark

from United Kingdom

Joined: 20 Feb 2004
Posts: 3434
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon May 23, 2005 8:13 pm    Post Subject:
Reply with quote Thanks

As has been pointed out it is safe to do, and I have seen this done, but I would make a suggestion to anyone doing this.

Where the 10mm and the legs of the ring meet I would fit a small enclosure housing (as this is a kitchen) a 32A 30mA RCBO, so the 10mm is effectively a sub-main. I would do this because at a later date, someone may uprate the source breaker as it feeds 10mm, and this could result in someone overloading the 2.5mm (you have no idea what they may do in the future).

When dropping a cable size, you should always add overload protection for the smaller cable, to no do so is bad practice, bad design and potentially inviting dangers that can be forseen and thus avoided.

__________________
I only do commercial and Industrial so Prescott can shove his Part P tax
Back to top
 Alert Moderators
BJC

from United Kingdom

Joined: 23 May 2005
Posts: 40
Location: Edinburgh,
United Kingdom
Thanked: 0 times

PostPosted: Mon May 23, 2005 8:23 pm    Post Subject:
Reply with quote Thanks

Thanks for that FWL_E. That tip could save me quite a bit of work. I've never used an RCBO (don't even know what it is) but don't imagine it's much different from an MCB.
Back to top
 Alert Moderators
Big_Spark

from United Kingdom

Joined: 20 Feb 2004
Posts: 3434
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon May 23, 2005 8:43 pm    Post Subject:
Reply with quote Thanks

BJ, an RCBO is simply a device that combines the functions of an RCD and an MCB in one neat package. They can be expensive compared to a simple MCB..£40 to £50 each, but they do provide total protection in the event of any type of fault occuring on the circuit.

A Two way enclosure, splah proof type, will be sufficient for your purposes.

Regardless fo the make of RCBO you Buy, I would suggest and MK enclosure, like this one (Part No: 5702s)



They look better than standard ones, but can withstand being in a kitchen without any undue influence from the environment they are in.

I would suggest a matched RCBO (Part No: 6932s)



I would further suggest that you do not buy these items from B&Q or any other shed, they will rob you blind, find your nearest Newey&Eyre or Edmundson Electrical, or similar dedicated wholesaler, you will save a significant amount on shed prices.

__________________
I only do commercial and Industrial so Prescott can shove his Part P tax
Back to top
 Alert Moderators
BJC

from United Kingdom

Joined: 23 May 2005
Posts: 40
Location: Edinburgh,
United Kingdom
Thanked: 0 times

PostPosted: Mon May 23, 2005 8:47 pm    Post Subject:
Reply with quote Thanks

I was just looking at that very housing and pondering whether it would do. Youv'e solved it all for me. Thanks. I've got an electric wholsesaler just around the corner so will purchase from them.

Thanks again.

Brian
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Testing of radial circuit,which feed an ring final circuit 21 1100 Tue May 20, 2008 11:13 am
radial ring 4 280 Sat May 03, 2008 6:50 pm
New elec oven - on radial/ring circuit 5 420 Tue Apr 22, 2008 11:54 am
Ring & Radial circuit regs 6 960 Wed Mar 22, 2006 11:36 pm
ring and radial 8 260 Wed Jul 02, 2008 8:12 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.