Hi folks was on here last month whilst I was away from home trying to figure out what was happening with my boiler.

Basically the system pressure was fluctuation between 0-0.5 bar to 2 bar, I've just got back and checked the Schrader valve on the top of the expansion vessel and got air, practically nothing but no water so am I right in saying the vessel looks sound?

I just popped a little air in there with the heating off and brought the pressure upto 0.5 bar cold and fired up the system which brought it upto 2 bar it's dropping off again so I presume the acid test would be to flatten the water side and charge the vessel to 0.5 bar then refill the heating loop and see how it fluctuates?

Thanks in advance
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
muggles

from United Kingdom

Joined: 28 Oct 2005
Posts: 4659
Location: Devon,
United Kingdom
Thanked: 616 times

PostPosted: Wed Feb 09, 2011 7:42 pm Reply with quote

Could just be residual air in the vessel, raise the c/h system pressure to 1.5 bar then press the schraeder again, see if you get water out of it before the pressure hits zero
Back to top
 Alert Moderators
Morris40

from United Kingdom

Joined: 09 Jan 2011
Posts: 231
Location: Middlesex,
United Kingdom
Thanked: 28 times

PostPosted: Wed Feb 09, 2011 7:42 pm Reply with quote

no that doesn't mean vessel is ok, it means that the diapragm is not knackered but what pressure air as in there, waht gauge did you use ? you probably need to re charge the vessel, you should have around 0.75 bar - 1.0 bar
Back to top
 Alert Moderators
Davie1888

from United Kingdom

Joined: 24 Jan 2011
Posts: 7
Location: Ayrshire,
United Kingdom

PostPosted: Wed Feb 09, 2011 8:02 pm Reply with quote

Hi I didn't measure the pressure cause there was basically nothing left, quick blast of air when I pressed the needle valve in then nothing, I just put a small amount of air in there to see if I got a pressure increase.

I took the system pressure to 0.5 with the water side full and cold on the boiler gauge, I've had it running upto max temp and the system pressure was at 2 bar I'm just waiting on the system temperature dropping to see what the pressure settles to!

According to the manual it came precharged to 0.5 bar, it's an 8 litre vessel so I know there's nowhere near that amount of air in there. I take it I'm trying to balance the air in the vessel against the water in the loop??

0.5 in air side with too much water in the water side would lead to high pressures??
Back to top
 Alert Moderators
rojaca

from United Kingdom

Joined: 14 Dec 2008
Posts: 745
Location: United Kingdom
Thanked: 80 times

PostPosted: Wed Feb 09, 2011 8:44 pm Reply with quote

you need to drain of htg side on blr. close iso's and drain using doc on lhs below pump. leave doc open whilst pressurising vesseland now fill it to between 0.75 to 1bar. close doc, open iso's refill htg , vent pump and you should be okay.

As muggles says before you do this I always put some extra pressure into system (up to about 2bar) then check schrader for water.
Back to top
 Alert Moderators
Davie1888

from United Kingdom

Joined: 24 Jan 2011
Posts: 7
Location: Ayrshire,
United Kingdom

PostPosted: Wed Feb 09, 2011 8:54 pm Reply with quote

Ok I'll stick some extra into the system tomorrow, it's settled back down to 0.5 bar so it looks pretty good initially.

By Iso's do you mean the supply and return valves for the heating loop. Is the doc a local drain within the boiler??

If I'm not sure I'll just get it limping over for now and get a local plumber in when I get paid!!

Cheers for the help guys much appreciated
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Problems with Baxi 105e combi despite new expansion vessel 8 820 Sun Dec 20, 2009 12:00 pm
Expansion vessel for Baxi Combo 105e 10 1780 Thu May 19, 2005 5:40 pm
baxi 105e expansion vessel recharge 4 920 Sat Jan 10, 2009 9:50 pm
Can I repressurize the expansion vessel of a Baxi 105e?? 4 800 Tue Feb 24, 2009 5:55 pm
Baxi boiler - Replacing Expansion Vessel 8 2060 Sun Dec 13, 2009 12:39 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.