2.5mm or 4.0mm
Reply with quote Thanks

I have three sockets off a 4.0mm radial circuit serving three bedrooms. Can I add an extra socket in each bedroom using 2.5mm cable. (The circuit breaker is 30amp.)
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
ryanj

from United Kingdom

Joined: 05 Oct 2003
Posts: 209
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Jul 28, 2005 11:23 am    Post Subject:
Reply with quote Thanks

No.

Use 4mm^2.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu Jul 28, 2005 11:36 am    Post Subject:
Reply with quote Thanks


__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
jabezz

from United Kingdom

Joined: 28 Jul 2005
Posts: 4
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Jul 28, 2005 11:37 am    Post Subject:
Thanks
Reply with quote Thanks

Thanks Ryan J for your quick response. I'll havta buy 4.00mm cable -- I had loads of 2.5mm leftover from a previous (ring main) job.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu Jul 28, 2005 11:42 am    Post Subject:
Reply with quote Thanks

If it had been a 2.5mm˛ ring final, on a 30A breaker, he could have spurred off a socket in each bedroom with a single piece of 2.5mm˛ cable.

As it is a 4mm˛ radial, on a 30A breaker, he cannot add a branch with a single piece of 2.5mm˛.

Discuss.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu Jul 28, 2005 11:47 am    Post Subject:
Reply with quote Thanks

ryanj wrote:
No.

Use 4mm^2.

Alternatively, yes if you use 2 x 2.5mm˛ of the same length.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
jabezz

from United Kingdom

Joined: 28 Jul 2005
Posts: 4
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Jul 28, 2005 11:48 am    Post Subject:
Link has too much
Reply with quote Thanks

Hi Ban-all-sheds -- thanks for the link in response to my question about 2.5mm or 4.00mm cable -- however this link has a lot of info -- which particular thing should I be looking at?

ban-all-sheds wrote:
http://www.diynot.com/forums/viewtopic.php?p=81696#81696
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu Jul 28, 2005 12:19 pm    Post Subject:
Reply with quote Thanks

That link should take you straight to the reference post called SIZING MCBs & CABLES - that's the one to read regarding this question....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
andy

from United Kingdom

Joined: 14 Sep 2004
Posts: 3972
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Jul 28, 2005 3:54 pm    Post Subject:
Reply with quote Thanks

ban-all-sheds wrote:
If it had been a 2.5mm˛ ring final, on a 30A breaker, he could have spurred off a socket in each bedroom with a single piece of 2.5mm˛ cable.

As it is a 4mm˛ radial, on a 30A breaker, he cannot add a branch with a single piece of 2.5mm˛.

Discuss.


because on the radial, you can continue to add more sockets to the extra socket, so 2.5 would overheat. where as on a ring main, your only susposed to take 1 spur which should not exceed 13A so 2.5 is OK
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Fri Jul 29, 2005 12:52 pm    Post Subject:
Reply with quote Thanks

10/10

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
jabezz

from United Kingdom

Joined: 28 Jul 2005
Posts: 4
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Jul 29, 2005 2:17 pm    Post Subject:
THANKS!
Reply with quote Thanks

Greatly appreciate each one who posted replies. I not only know what to do, but also the WHY!

It so much more reassuring to learn the reason behind a standard, knowing it's not just some arbitrary rule.

Thanks!
Back to top
 Alert Moderators
streethawk

from United Kingdom

Joined: 11 Aug 2006
Posts: 4
Location: Lincolnshire,
United Kingdom
Thanked: 0 times

PostPosted: Fri Aug 11, 2006 7:40 pm    Post Subject:
Reply with quote Thanks

ryanj wrote:
No.

Use 4mm^2.


but i can't get 4mm anywhere anymore... what am i meant to use - 6mm? bit excessive, surely!
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Fri Aug 11, 2006 7:55 pm    Post Subject:
Reply with quote Thanks

Have you tried:
http://www.tlc-direct.co.uk/Main_Index/Cable_Index/Twin_and_Earth/index.html

BTW the post you are replying to is over 12months old.
Back to top
 Alert Moderators
fireman22

from United Kingdom

Joined: 18 Mar 2005
Posts: 605
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Aug 11, 2006 10:49 pm    Post Subject:
Reply with quote Thanks

jabezz, if you are only feeding a few bedroom sockets and you have central heating i imagine the load will be quite low so you could run 2.5mm radials and lower the amp rating of the mcb to 20A. but if you had an overload problem later this could be a pain. if you can get back to the fuse board you could change this circuit to a 32A ring using the 4mm cable as the first leg of the ring then from the last socket in 4mm round the rest in 2.5 then back to the board.
Back to top
 Alert Moderators
streethawk

from United Kingdom

Joined: 11 Aug 2006
Posts: 4
Location: Lincolnshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat Aug 12, 2006 3:57 pm    Post Subject:
Reply with quote Thanks

Spark123 wrote:
Have you tried:
http://www.tlc-direct.co.uk/Main_Index/Cable_Index/Twin_and_Earth/index.html

BTW the post you are replying to is over 12months old.


I hadn't, no just the obvious suspects - wickes, screfix etc.

thanks for that

age is in the mind btw icon_wink.gif
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.