shower

This topic originated from the How to page called Miniature circuit breakers (MCBs)
Click here to return to the page called Miniature circuit breakers (MCBs).
Goto page 1, 2, 3  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
westside

from United Kingdom

Joined: 03 Aug 2005
Posts: 25
Location: Liverpool,
United Kingdom
Thanked: 0 times

PostPosted: Wed Aug 03, 2005 7:27 pm    Post Subject:
shower
Reply with quote Thanks

hi, i have installed a new electric shower 10.8 kw. Wired it to the double pole with 10m2 cable. Its all set bar being connected to the cu.
Reason being i want to know is the mcb high enough for the shower.
MCB is a(mem 32a type b),
cu is 240/415v- 50hz.
the 10m2 cable was already there and a sticker on the mcb saying shower.
will it be alright.
thankful for any advice icon_confused.gif
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
comms

from United Kingdom

Joined: 13 Nov 2004
Posts: 828
Location: Berkshire,
United Kingdom
Thanked: 0 times

PostPosted: Wed Aug 03, 2005 7:33 pm    Post Subject:
Reply with quote Thanks

power(kw)/volts(230)=amps

10.8kw / 230 volt = 46.9amp

So no the 32amp mcb will not be sufficient.
Back to top
 Alert Moderators
westside

from United Kingdom

Joined: 03 Aug 2005
Posts: 25
Location: Liverpool,
United Kingdom
Thanked: 0 times

PostPosted: Wed Aug 03, 2005 7:40 pm    Post Subject:
Reply with quote Thanks

so i need a 46.9amp mcb then.
also could i put it into the cooker mcb as i do not use it.
Back to top
 Alert Moderators
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4538
Location: United Kingdom
Thanked: 10 times

PostPosted: Wed Aug 03, 2005 7:49 pm    Post Subject:
Reply with quote Thanks

You need a 50A MCB

Please tell us how long this cable is, and what route it takes, and whether you are going to have rcd protection on this circuit,

oh I think I hear something, *listens carefully* sounds like ban shouting something about pee, *replies "not on the CU, ban, would be painful I'd imagine "* icon_lol.gif
Back to top
 Alert Moderators
westside

from United Kingdom

Joined: 03 Aug 2005
Posts: 25
Location: Liverpool,
United Kingdom
Thanked: 0 times

PostPosted: Wed Aug 03, 2005 7:55 pm    Post Subject:
Reply with quote Thanks

it`s about 50 ft long
it goes from my sitting room up to the attic then along to the bathroom on the other side of the house ( were i found it taped up).
how do i put a rcd in and were in the cu does it go.
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Wed Aug 03, 2005 8:35 pm    Post Subject:
Reply with quote Thanks

easiest way to fit an RCD is to cut the shower cable where it leaves the CU, get a shower RCD mini-consumer unit and fit this in-line with the shower cable. You're sure the entire cable run is 10mm2? It needs to be, given this rating and distance.

Some may argue use 16mm2 cable, and a 63A industrial isolator instead of that pull-switch, but in reality, you're likely to be ok with 10mm, as long as its ventilated (not buried in loft insulation), and the 45A pullswitch.
Back to top
 Alert Moderators
comms

from United Kingdom

Joined: 13 Nov 2004
Posts: 828
Location: Berkshire,
United Kingdom
Thanked: 0 times

PostPosted: Wed Aug 03, 2005 8:47 pm    Post Subject:
Reply with quote Thanks

Instead of using an rcd you could replace the mcb for a rcbo, this will save you having to install the second shower cu.
Back to top
 Alert Moderators
BenStiller

from United Kingdom

Joined: 23 May 2005
Posts: 207
Location: Liverpool,
United Kingdom
Thanked: 0 times

PostPosted: Wed Aug 03, 2005 8:53 pm    Post Subject:
Reply with quote Thanks

I would put a 45 amp breaker in, and you might not need an rcd, it depends on your earthing system
Back to top
 Alert Moderators
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23346
Location: Sussex,
United Kingdom
Thanked: 5 times

PostPosted: Wed Aug 03, 2005 8:54 pm    Post Subject:
Reply with quote Thanks

crafty1289 wrote:
and the 45A pullswitch.


(breezer strokes chin) hmmm

comms wrote:
power(kw)/volts(230)=amps

10.8kw / 230 volt = 46.9amp


icon_idea.gif this

__________________
Do you like music Mr Finch?
Forum = Opinions
Back to top
 Alert Moderators
westside

from United Kingdom

Joined: 03 Aug 2005
Posts: 25
Location: Liverpool,
United Kingdom
Thanked: 0 times

PostPosted: Wed Aug 03, 2005 11:09 pm    Post Subject:
Reply with quote Thanks

sorry about replying so late, yes it`s defo 10m2 cable and its not covered,
its just lying on the loft floor.
i just found in the cu a elcb,
apart from upgrading the mcb to 50amp, should the elcb be ok
thanks for the input icon_redface.gif
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Wed Aug 03, 2005 11:18 pm    Post Subject:
Reply with quote Thanks

What are the current ratings of the ELCB (trip and capacity)? What else does the ELCB supply feed? The reason I ask is to determine if there is enough capacity left in it to run the shower. The 10mm˛ cable should be good for 64A if installed away from insulation.
Back to top
 Alert Moderators
mapj1

from United Kingdom

Joined: 24 Nov 2004
Posts: 1040
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Aug 03, 2005 11:54 pm    Post Subject:
Reply with quote Thanks

Quote:
sorry about replying so late,

Its OK, we have gone to bed and will respond tommorrow if you are lucky.
icon_eek.gif icon_biggrin.gif icon_lol.gif
Seriously, with Email and bbs like this no one waits up for you to post, so dont feel guilty. There are some night owls here.
Seriously wait and see if anyone has any more thoughts tommorrow before rushing off. If they don't its probably sensible as alerady said.

__________________
regards Mike(G7VZY)
-STICKY Reference Info @ top of forum, Has diagrams & answers to common probs-
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21980
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu Aug 04, 2005 9:43 am    Post Subject:
Reply with quote Thanks

1) Firstly, that rating will almost certainly be a 240V one, i.e. 45A.

2) I know I am well overdue in editing my "This is Part P" document, but DIYnot have not said they'll post it as I suggested, so I think we do have to highlight to westside that if he does this without notifying LABC in advance then he is breaking the law. We may not care, but he might...

3) Westside - you don't know the difference between metres and millimeters, you have no idea of the relationship between voltage, current and power, you have no idea what electrical specifications mean, you don't know how to fit things into a CU and you don't know where an RCD would go in the circuit.

Are you sure you should be doing this job?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
westside

from United Kingdom

Joined: 03 Aug 2005
Posts: 25
Location: Liverpool,
United Kingdom
Thanked: 0 times

PostPosted: Thu Aug 04, 2005 5:04 pm    Post Subject:
Reply with quote Thanks

hi people, again sorry for late reply as went to bed cuz got work.
To be honest it`s my wifes dads friend who is a retired electrician and has`nt done work for years.
That`s why i`m asking for answers so i can understand what he is doing.
In the cu the elcb says on it
curent trip rating 0.1a
1th=40a
240/415v 50hz
The elcb wires are only going into the meter.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21980
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu Aug 04, 2005 6:43 pm    Post Subject:
Reply with quote Thanks

westside wrote:

In the cu the elcb says on it

curent trip rating 0.1a - that's 100mA, better than nothing, but not sensitive enough for a shower - 30mA is recommended
1th=40a - that means it can only interrupt 40A - not beefy enough for the shower, let alone an entire installation, which it probably used to cover
The elcb wires are only going into the meter - so it's disconnected anyway.

So is there no RCD anywhere in the CU?

Do you know what type of earthing your supply has? A 100mA RCD for the whole thing sounds like it might be TT...

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2, 3  Next
Page 1 of 3

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Oven, hob & Shower installation in old bungalow in Irela 5 200 Fri Jan 11, 2008 9:09 pm
water in ducting from shower extractor fan 3 1920 Thu Jan 10, 2008 5:22 pm
Shower fairies! 7 440 Wed Jan 09, 2008 9:00 pm
had a shower fitted is this safe! 22 1440 Sun Jan 13, 2008 10:46 am
shower keeps tripping, can anyone help? 8 420 Sun Jan 13, 2008 12:12 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.