Shower help req
Reply with quote Thanks

Hi I'm needing to buy a new shower I have a wylex 30 amp mcb like the one in the link at the foot of page I would like to put in a 9.5 kw can I change the 30A mcb to a 40A mcb just by removing the 30a from the fuse box and putting in the 40a one.Thanks



http://www.thefusecompany.com/fuse.php/cPath/58/products_id/398
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Mon Sep 12, 2005 8:09 pm    Post Subject:
Reply with quote Thanks

Yes, but dont use that company.

You will need to remove the cover from the consumer unit in order to fit the new MCB.
Back to top
 Alert Moderators
baldelectrician

from United Kingdom

Joined: 27 Jul 2005
Posts: 479
Location: Ayrshire,
United Kingdom
Thanked: 3 times

PostPosted: Mon Sep 12, 2005 8:10 pm    Post Subject:
Shower
Reply with quote Thanks

Only if the cable will take the load under the conditions

If it's 6mm then it almost definately wont do
Back to top
 Alert Moderators
bobbyjay

from United Kingdom

Joined: 12 Sep 2005
Posts: 4
Location: Lanarkshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Sep 12, 2005 8:15 pm    Post Subject:
Reply with quote Thanks

It's 6mm cable I have on the shower that's there already.Is there any other company I can use for this type of mcb or any other way i can redo it without changing the mcb thanksagain.
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Mon Sep 12, 2005 8:17 pm    Post Subject:
Reply with quote Thanks

Screwfix should have them, and TLC, even B&Q but dont tell ban i said that
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Mon Sep 12, 2005 8:42 pm    Post Subject:
Reply with quote Thanks

haven't seen that style of mcb in B&Q they have the modern wylex and the wylex standard but not the NN style that he posted a link to.

TLC have them but they aren't that much cheaper than the fuse company http://www.tlc-direct.co.uk/Main_Index/Consumer_Units_Index/Wylex_NN_Range/index.html (the headline price is cheaper but you'd have to compare delivery charges if vat is included etc to find out which was really cheaper)
Back to top
 Alert Moderators
bobbyjay

from United Kingdom

Joined: 12 Sep 2005
Posts: 4
Location: Lanarkshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Sep 13, 2005 8:32 am    Post Subject:
Re: Shower
Reply with quote Thanks

baldelectrician wrote:
Only if the cable will take the load under the conditions

If it's 6mm then it almost definately wont do


Is that the cable running from mcb to shower or incoming from the meter side I know it has to be replaced to 10 mm running from the mcb. Thanks again.
Back to top
 Alert Moderators
photon

from United Kingdom

Joined: 03 Aug 2005
Posts: 16
Location: Fife,
United Kingdom
Thanked: 0 times

PostPosted: Tue Sep 13, 2005 8:58 am    Post Subject:
Reply with quote Thanks

Loads of Wylex MCB on eBay. Usually fairly cheap.

Just make sure you buy from a rated seller.

(and avoid the ones where the MCB has that dark brown crispy look .... icon_lol.gif )


If you intend to uprate the cable to the shower consider fitting an in line RCD. (you dont mention having one in the main CU)
Back to top
 Alert Moderators
bobbyjay

from United Kingdom

Joined: 12 Sep 2005
Posts: 4
Location: Lanarkshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Sep 13, 2005 9:19 am    Post Subject:
Reply with quote Thanks

Sorry about that never thought the whole mcb board is protected by a RCD switch
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21979
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Tue Sep 13, 2005 12:31 pm    Post Subject:
Re: Shower
Reply with quote Thanks

bobbyjay wrote:
Is that the cable running from mcb to shower or incoming from the meter side I know it has to be replaced to 10 mm running from the mcb. Thanks again.

If your meter tails are only 6mm˛, or even 10mm˛, then you've got more important things to sort out before you fit a new shower...

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Shower fairies! 7 440 Wed Jan 09, 2008 9:00 pm
Connect Underfloor Heating from Shower Swicth 12 800 Wed Jan 09, 2008 3:42 pm
Another shower cable query! 2 380 Wed Jan 09, 2008 2:40 am
water in ducting from shower extractor fan 3 1920 Thu Jan 10, 2008 5:22 pm
Oven, hob & Shower installation in old bungalow in Irela 5 200 Fri Jan 11, 2008 9:09 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.