Earth Loop Impedance


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
Maboza-Ritchy

from United Kingdom

Joined: 18 Sep 2005
Posts: 92
Location: Ayrshire,
United Kingdom

PostPosted: Thu Oct 06, 2005 6:30 pm Reply with quote

Hi
Can any of you explain, or recommend sites that can explain earth loop impedance, the theory & testing? I never got the hang of it during my day release classes which was many years ago.

BTW this a great site, only found it a couple of weeks agop.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Lectrician

from United Kingdom

Joined: 18 Jul 2004
Posts: 7514
Location: Devon,
United Kingdom
Thanked: 277 times

PostPosted: Thu Oct 06, 2005 6:47 pm Reply with quote

Resistance from the live to earth, via the supply cables and transformer.

Using ohms law, you can determine the fault current in amps, that would flow if a dead short was introduced. This is the current that would flow down the earth to the substation, and back up the live to your fuse, as the fuse blows.

The lower the earth loop, the higher the PFC (prospective fault current).

The higher the PFC, the quicker the fuse will blow.

We need to therefor know the earth loop (Ze at origin, Zs at circuit end) to determine weather the fuse/mcb will operate quickly enough to give disconnection with in the time stated in regs (0.2, 0.4 or 5 seconds, depending on circuit type and location).

A TN-S or TN-C-S system will give nice low resistances, the REC state that for a TN-S system, the max Ze they will provide will be 0.8ohm. For TN-C-S it will be no more that 0.35ohm.

For a TT system, the earth rod will generally give a higher resistance, and therefore will not provide a high enough fault current to operate the fuse/mcb quickly enough to conply to the regs. This is why on TT systems, an RCD is essential.
Back to top
 Alert Moderators
Maboza-Ritchy

from United Kingdom

Joined: 18 Sep 2005
Posts: 92
Location: Ayrshire,
United Kingdom

PostPosted: Thu Oct 06, 2005 7:15 pm Reply with quote

Thanks for the speedy response.

Lectrician wrote:
Resistance from the live to earth, via the supply cables and transformer.


Can you explain further - how is the resistance between the live and earth measured? Should this resistance not be at infinity or very close to it?

Thanks in advance.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 24950
Location: Cheshire,
United Kingdom
Thanked: 426 times

PostPosted: Thu Oct 06, 2005 7:21 pm Reply with quote

I know you - you're Lionel's brother - Maballsa Ritchie! icon_lol.gif
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 46974
Location: London,
United Kingdom
Thanked: 1706 times

PostPosted: Thu Oct 06, 2005 7:26 pm Reply with quote

Maboza-Ritchy wrote:
Can you explain further - how is the resistance between the live and earth measured? Should this resistance not be at infinity or very close to it?

You might be saying that because you missed a word out of your question.

Earth Fault Loop Impedance.

You want to know what the impedance will be if you were to get a L/E fault, because if it is too high then the protective device will not operate quickly enough. This is a Bad Thing™.

Re sites - try these:

http://www.tlc-direct.co.uk/Book/5.1.1.htm

http://www.tlc-direct.co.uk/Book/8.1.1.htm
Back to top
 Alert Moderators
Maboza-Ritchy

from United Kingdom

Joined: 18 Sep 2005
Posts: 92
Location: Ayrshire,
United Kingdom

PostPosted: Thu Oct 06, 2005 9:06 pm Reply with quote

securespark wrote:
I know you - you're Lionel's brother - Maballsa Ritchie! icon_lol.gif


Your right! Maboza is the scottish equivalent of Maballsa. It's the same as Tom and Tam, Willie and Wullie etc.
Back to top
 Alert Moderators
Maboza-Ritchy

from United Kingdom

Joined: 18 Sep 2005
Posts: 92
Location: Ayrshire,
United Kingdom

PostPosted: Thu Oct 06, 2005 9:19 pm Reply with quote

Ban
Thanks for the reply and link to the site. I'm going to hit the sack (early bedder) for now but will it check it out tomorrow.
Thanks again for swift reply.

Ciao Maboza (Maballsa)
Back to top
 Alert Moderators
slippyr4

from United Kingdom

Joined: 12 Jul 2005
Posts: 767
Location: Bedfordshire,
United Kingdom
Thanked: 4 times

PostPosted: Fri Oct 07, 2005 7:18 am Reply with quote

This thread reminds me to ask a question that i've been wondering for a while. It's an out of interest thing only...

Quote:
the REC state that for a TN-S system, the max Ze they will provide will be 0.8ohm


If your TN-S Ze is > 0.8 ohm, are the REC obliged to fix it, or can/will they just re-designate it a TT supply and leave it to the customer to get an earth rod & RCD ?
Back to top
 Alert Moderators
Lectrician

from United Kingdom

Joined: 18 Jul 2004
Posts: 7514
Location: Devon,
United Kingdom
Thanked: 277 times

PostPosted: Fri Oct 07, 2005 2:55 pm Reply with quote

They are not obliged to provide an earthing terminal. So if it involved excessive re-cabling, and not locating a high resistance joint (for example), I think they would remove their earth terminal, and tell you to sort your own!!
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Earth Loop Impedance readings 16 280 Fri Aug 17, 2012 7:31 pm
testing earth fault loop impedance 20 43960 Tue Aug 30, 2005 6:37 pm
high earth loop impedance 24 360 Tue Jan 17, 2012 9:53 am
earth loop impedance reading 4 1080 Sun Sep 25, 2005 1:03 pm
Earth loop impedance on TT? 13 900 Sun Mar 19, 2006 8:40 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.