andy Mullin

from United Kingdom

Joined: 05 Dec 2005
Posts: 2
Location: Staffordshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Dec 05, 2005 11:41 pm    Post Subject:
Electric Showers
Reply with quote Thanks

i have a 10.5 kw showerand need to run a cable some 25 meters one electrician says 10 mm Twin & earth will suffice but others say it should be 16mm. i am led to believe that 10mm goes up to 9.5kw. any advice would be welcome
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
supersparks

from United Kingdom

Joined: 28 Oct 2003
Posts: 586
Location: Hertfordshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Dec 06, 2005 12:04 am    Post Subject:
Reply with quote Thanks

at 25 meters your right on the edge...litrally at 26 meters it wont comply, id install 16mm personally
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21983
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Tue Dec 06, 2005 2:39 am    Post Subject:
Reply with quote Thanks

I get it going non-compliant at 22.1m, assuming 0.8 ohms Ze and a B50 - where am I going wrong?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Big_Spark

from United Kingdom

Joined: 20 Feb 2004
Posts: 3434
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Dec 06, 2005 6:25 am    Post Subject:
Reply with quote Thanks

Not sure of when the non-compliance kicks in, but manually calculating at 25 m and using my cbale calc software the cable must be 16mm² for compliance.

So kick the 10mm² into touch and go with 16mm²
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21983
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Tue Dec 06, 2005 10:44 am    Post Subject:
Reply with quote Thanks

Big_Spark wrote:
Not sure of when the non-compliance kicks in, but manually calculating at 25 m and using my cbale calc software the cable must be 16mm² for compliance.

Did it say why?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
arctic

from United Kingdom

Joined: 10 Feb 2004
Posts: 108
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Dec 06, 2005 10:46 am    Post Subject:
Reply with quote Thanks

where's it being run?
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21983
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Tue Dec 06, 2005 10:55 am    Post Subject:
Reply with quote Thanks

If it's distance related it's not an installation method or other de-rating issue...

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
smokeyJoe

from United Kingdom

Joined: 23 Nov 2005
Posts: 16
Location: Cheshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Dec 06, 2005 5:23 pm    Post Subject:
Reply with quote Thanks

Which rule(s) are we using to determine compliance here?
voltage drop (525-01-02)?
disconnection time assuming a TN system (413-02-08)?
impedance of the protective conductor to the main equipotential bond with a guess at the type of protective device (413-02-13)?
Please point me at the relevant chapter.
Is there really enough information here to make a sound decision?
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21983
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Tue Dec 06, 2005 7:22 pm    Post Subject:
Reply with quote Thanks

smokeyJoe wrote:
Which rule(s) are we using to determine compliance here?
voltage drop (525-01-02)?

It shouldn't be hard to establish that it isn't that....

Quote:
disconnection time assuming a TN system (413-02-08)?
impedance of the protective conductor to the main equipotential bond with a guess at the type of protective device (413-02-13)?

Those two are effectively the same, and assuming TN-S & B50 was how I got to 22.1m

Can't remember the figure for TN-C-S but it was a lot more....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Tue Dec 06, 2005 8:54 pm    Post Subject:
Reply with quote Thanks

10mm² XLPE SWA? anyone?
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21983
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Tue Dec 06, 2005 9:24 pm    Post Subject:
Reply with quote Thanks

XLPE SWA is only rated as high as it is because the insulation can tolerate higher temperatures.

Run conductors at 90°C into normal switches and shower terminal blocks and expect trouble....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16480
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Tue Dec 06, 2005 9:46 pm    Post Subject:
Reply with quote Thanks

ban-all-sheds wrote:
Can't remember the figure for TN-C-S but it was a lot more....


Mmmmm. PME has Ze of 0.35Ohm. It will be much higher.

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
Big_Spark

from United Kingdom

Joined: 20 Feb 2004
Posts: 3434
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Dec 06, 2005 10:07 pm    Post Subject:
Reply with quote Thanks

ban-all-sheds wrote:
XLPE SWA is only rated as high as it is because the insulation can tolerate higher temperatures.

Run conductors at 90°C into normal switches and shower terminal blocks and expect trouble....


BAS..the reason SWA XLPE or PVC/PVC has a higher current rating is actually due to the copper the cable is made from.

T&E is soft drawn annealed copper that is only 98% pure for compliance with the relevent BS, however SWA XLPE or PVC/PVC is hard-drawn annealed and 99.1% pure as a minimum..typically most seem to be about 99.4% pure copper..

The annealing process has an effect on the current carrying capacity of the cable, the insulation has a minor effect, but not to the extent that exists...

I do agree with the 90°C comment however..but if you ever find that in your home I think you'll already be dead.. icon_lol.gif
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21983
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Wed Dec 07, 2005 12:31 am    Post Subject:
Reply with quote Thanks

securespark wrote:
ban-all-sheds wrote:
Can't remember the figure for TN-C-S but it was a lot more....


Mmmmm. PME has Ze of 0.35Ohm. It will be much higher.

That's what I said. I can't remember how much higher, and I can't be **sed to work it out again. I have a vague memory that volt-drop kicked in at a lower figure anyway.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21983
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Wed Dec 07, 2005 1:10 am    Post Subject:
Reply with quote Thanks

Big_Spark wrote:
BAS..the reason SWA XLPE or PVC/PVC has a higher current rating is actually due to the copper the cable is made from.

T&E is soft drawn annealed copper that is only 98% pure for compliance with the relevent BS, however SWA XLPE or PVC/PVC is hard-drawn annealed and 99.1% pure as a minimum..typically most seem to be about 99.4% pure copper..

The annealing process has an effect on the current carrying capacity of the cable, the insulation has a minor effect, but not to the extent that exists...


10mm² 2-core cables, single-phase, Reference Method 1:

4D2A 70°C Thermoplastic 63A
4D5A 70°C Thermoplastic (T/E) 64A
4D4A 70°C Thermoplastic SWA 67A
4E4A 90°C Thermosetting SWA 85A, together with a note to say that if you need the conductors to operate at 70°C you should use the 4D4A figure....

So I'll have to accept that the conductor material makes a slight difference (approx 5 or 6%) to the capacity.

And you'll have to accept that "the insulation has a minor effect, but not to the extent that exists" is wrong, as the ability to operate at 90°C adds another 27% to the capacity (67A -> 85A).

Quote:
I do agree with the 90°C comment however..but if you ever find that in your home I think you'll already be dead.. icon_lol.gif
Meaningless.

You'd be dead if the ambient temperature got to 70°C too.

If you ran 85A through your 10mm² XLPE SWA, the conductor temperature would reach 90°C. You wouldn't die from that, but you might get some unfortunate consequences (probably not including fire, at least not immediately) if that conductor was screwed into something not designed to operate at 90°C.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Electric Showers - Advice 5 3560 Tue Mar 22, 2005 9:50 am
2 electric showers 2 300 Fri Aug 24, 2007 11:18 am
Electric showers - do they have an integral pump?? 13 720 Tue Jan 03, 2006 10:17 am
Electric Showers - maximum cable lengths 7 680 Sat Nov 04, 2006 2:14 am
electric showers 8 2820 Mon Aug 28, 2006 5:53 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.