Joined: 02 Jan 2006 Posts: 13 Location: Yorkshire, United Kingdom Thanked: 0 times
Posted: Mon Jan 02, 2006 3:21 pm Post Subject:
cooker cable
Just wired a 4.25kw double oven to a spare 30amp fuse on CU.I`ve used 2.5T&E from CU to terminal box near oven.From here used 2.5mm heat resistant flex to oven, as reccomended by oven instruction booklet.The T&E used from CU totals approx 3.5m in length.Would this be considered as safe? According to \\\"home\\\" section of site 2.5mm is fine up to 4800W &20A!
Joined: 05 Jun 2005 Posts: 707 Location: Birmingham, United Kingdom Thanked: 0 times
Posted: Mon Jan 02, 2006 3:25 pm Post Subject:
Re: cooker cable
gedantic wrote:
Just wired a 4.25kw double oven to a spare 30amp fuse on CU.I`ve used 2.5T&E from CU to terminal box near oven.From here used 2.5mm heat resistant flex to oven, as reccomended by oven instruction booklet.The T&E used from CU totals approx 3.5m in length.Would this be considered as safe? According to \\\"home\\\" section of site 2.5mm is fine up to 4800W &20A!
note the highlighted bits and then comment on what you see
Joined: 20 Feb 2004 Posts: 3434 Location: United Kingdom Thanked: 0 times
Posted: Mon Jan 02, 2006 3:31 pm Post Subject:
Couple of points..2.5T&E can certainly handle the loading as it is around 18A at 230V or 17.5A at 240V.
However, the cable is not rated at 30A and so it should not be on a 30A breaker so you should change this to 20A.
Further, what is the distance from the consumer unit to the cooker outlet plate? So long as the cable run is shorter than about 27 meters total length you will be OK for volt drop..and being domestic I would presume that this is not an issue..
Joined: 02 Jan 2006 Posts: 13 Location: Yorkshire, United Kingdom Thanked: 0 times
Posted: Mon Jan 02, 2006 3:42 pm Post Subject:
Re: cooker cable
[quote="pdcelec"]
gedantic wrote:
Just wired a 4.25kw double oven to a spare 30amp fuse on CU.I`ve used 2.5T&E from CU to terminal box near oven.From here used 2.5mm heat resistant flex to oven, as reccomended by oven instruction booklet.The T&E used from CU totals approx 3.5m in length.Would this be considered as safe? According to \\\"home\\\" section of site 2.5mm is fine up to 480ote the highlighted bits aYnd then comment on what you see
Joined: 02 Jan 2006 Posts: 13 Location: Yorkshire, United Kingdom Thanked: 0 times
Posted: Mon Jan 02, 2006 3:47 pm Post Subject:
Big_Spark wrote:
Couple of points..2.5T&E can certainly handle the loading as it is around 18A at 230V or 17.5A at 240V.
However, the cable is not rated at 30A and so it should not be on a 30A breaker so you should change this to 20A.
Further, what is the distance from the consumer unit to the cooker outlet plate? So long as the cable run is shorter than about 27 meters total length you will be OK for volt drop..and being domestic I would presume t hat this is not an issue..
Affirmative! So all I need do is change the fuse wire from 30 to 20?
Joined: 17 Jun 2004 Posts: 4538 Location: United Kingdom Thanked: 10 times
Posted: Mon Jan 02, 2006 3:52 pm Post Subject:
gedantic wrote:
Affirmative! So all I need do is change the fuse wire from 30 to 20?
No, you need to change the whole fuse (and the base), what happens if the 20A blows for whatever reason and the person fixing it sees a 30A carrier, doesn't realise what has been done and fits 30A fuse wire?
Might be easier to purchase a 20A plug in MCB for it though, than a 20A BS3036
Joined: 02 Jan 2006 Posts: 13 Location: Yorkshire, United Kingdom Thanked: 0 times
Posted: Mon Jan 02, 2006 4:12 pm Post Subject:
Adam_151 wrote:
gedantic wrote:
Affirmative! So all I need do is change the fuse wire from 30 to 20?
No, you need to change the whole fuse (and the base), what happens if the 20A blows for whatever reason and the person fixing it sees a 30A carrier, doesn't realise what has been done and fits 30A fuse wire?
Might be easier to purchase a 20A plug in MCB for it though, than a 20A BS3036
Your knowledge is very much appreciated.Thanks again!