What size cable

Joined
20 Jan 2006
Messages
7
Reaction score
0
Location
Lancashire
Country
United Kingdom
I have just bought a 10.9 - 11.8kw electric cooker it has a ceramic hob a top and bottom oven, what rating of cable do I need? Will 6 mm or 10 mm twin & earth be sufficient? Thankyou
 
Sponsored Links
I have just bought a 10.9 - 11.8kw electric cooker it has a ceramic hob a top and bottom oven, what rating of cable do I need? Will 6 mm or 10 mm twin & earth be sufficient? Thankyou
The diversity factor of any cooker is the first 10amps + 30% of the rest I make this to be a total of 30Amps (inc socket outlet) therefor 6mm should be fine however you could always wire it in 10mm just to be sure or it's a long run to the CCU.
 