I am trying to get my head around the new loop impedance figures. We would set the step down transformer to an open circuit voltage of 230 volt plus 10% = 253 volt and we were allowed a volt drop of 230 minus 6% = 216.2 volt but the loop impedance at this point can not exceed 0.35 Ω.
A B type MCB needs 5 times the rated current to flow so taking a B32 as an example at 253 volts a loop impedance of 1.58125 Ω is required. Since we measure total earth loop impedance not just that within the installation it is the voltage at the transformer which matters not the voltage at the house.
The volts could be 230 which would mean the loop impedance could be 1.4375 Ω however at the transformer it is unlikely the volts would have dropped below that level. Until we start to consider micro generation then in order to feed into the grid the transformer voltage may be set lower.
Clearly at night solar panels will not generate and wind power will also at some point stop even the sterling generators fitted to central heating boilers will likely not be running in the summer so the transformer will never be set to 216.2 volts although the supply to house may reach that point.
So case scenario is 216.2 volts with a loop impedance of 0.35 Ω (TN-C-S) so with a 100A supply the transformer would need to be 35 volt above that value so transformer volts would be 251.2 volts. For the transformer volts to be set at 230 the loop impedance would need to be 0.15 Ω approx.
I realise micro generation can mean the step down transformer is set to a lower voltage and that we are not considering just one house but a line of houses but I fail to see how the short circuit current at a loop impedance of 1.44 Ω would drop below the 160A mark even with micro generation lowering the transformer voltage.
I realise it requires Norton's theorem or Thévenin's theorem to truly work out the short circuit current it is not a single house. But just can't see why we have the reduction?