Hi all,
I am planning to install electric under floor heating under tiles in our new ensuite bathroom (500w total). One problem I have is that the easiest way to feed the Thermostat/timer is via a Fused spur from a (RCD protected)ring main cable that runs under the floor along the outside wall. This therfore requires the thermostat to be sited within the bathroom on the same wall. All manufacturers, except 1 state that their thermostats must be fitted outside of bathrooms to meet wiring regulations. However, one manufacturer (Heat Mat) states that their unit has a protection rating of "IP21" and that this allows fitting within a bathroom. This is ideal for me but I am unable to verify this claim by searches on the web etc. This forms part of a greater build project which will have to be Elecrically certificated before I get the building signed off. Can anyone advise please?
Also, as the ring concerned is RCD protected at the distribution box, am I correct in fitting a starightforward spur rather the RCD spur?

Thanks
Derek
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10753
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Fri Apr 14, 2006 3:41 pm    Post Subject:
Reply with quote Thanks

The normal way we connect under floor heating is to set a temperature probe into the tile adhesive along with the heat mats / wires. This is then connected to a controller, programmer and spur all located outside the bathroom. In your situation an RCD spur is not nessacery as the circuit you will be connecting to is already protected by an RCD.

Rob
Back to top
 Alert Moderators
Derek S

from United Kingdom

Joined: 14 Apr 2006
Posts: 2
Location: Hampshire,
United Kingdom
Thanked: 0 times

PostPosted: Fri Apr 14, 2006 4:31 pm    Post Subject:
Reply with quote Thanks

RF Lighting wrote:
The normal way we connect under floor heating is to set a temperature probe into the tile adhesive along with the heat mats / wires. This is then connected to a controller, programmer and spur all located outside the bathroom. In your situation an RCD spur is not nessacery as the circuit you will be connecting to is already protected by an RCD.

Rob


Excellent - thanks. This is the route we are forced into now anyway as further research (on this forum) has identified that the IP21 rated controller could be fitted in the bathroom, but only in zone 3. My planned position unfortunately lies in zone 2 so is a no goer. Luckily I can follow your lead and feed it from the other side of an internal wall with a spur off the ring that feeds the shaver point.

Again thanks
Derek
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
towel rail & underfloor heating in bathroom 8 240 Tue Mar 10, 2009 11:57 am
Positioning of bathroom underfloor heating controls 2 1080 Tue Nov 14, 2006 9:13 pm
Underfloor Heating (Bathroom) 3 540 Thu May 03, 2007 9:00 am
Bathroom Underfloor Heating 6 800 Wed Jun 27, 2007 6:08 pm
Underfloor heating bathroom 6 700 Mon Jan 09, 2006 3:16 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.