Bathroom fan from two switches
Reply with quote Thanks

Putting in fan and would like to know if its possible and how to wire it so it works off both the light switch and the shower switch.Doing it this way so it can be used from either one.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12857
Location: Yorkshire,
United Kingdom
Thanked: 22 times

PostPosted: Sun Jul 23, 2006 12:11 pm    Post Subject:
Reply with quote Thanks

no










unless you are familiar with relays, and a type of relay that can have 2 inputs to energise the controlled circuit. not sure if such an item exists, TBH.
Back to top
 Alert Moderators
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23346
Location: Sussex,
United Kingdom
Thanked: 5 times

PostPosted: Sun Jul 23, 2006 12:17 pm    Post Subject:
Re: Bathroom fan from two switches
Reply with quote Thanks

donetello wrote:
Putting in fan and would like to know if its possible and how to wire it so it works off both the light switch and the shower switch.Doing it this way so it can be used from either one.


as the above post says.

it can be done by it will require relays and housings for said relays and fcu.s in essence its best just to either have the fan switch on with the lights, independantly or have a humidty fan that switches on / off acording to the room humidity

__________________
Do you like music Mr Finch?
Forum = Opinions
Back to top
 Alert Moderators
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4540
Location: United Kingdom
Thanked: 10 times

PostPosted: Sun Jul 23, 2006 2:51 pm    Post Subject:
Reply with quote Thanks

crafty1289 wrote:

and a type of relay that can have 2 inputs to energise the controlled circuit. not sure if such an item exists, TBH.


You could just use two of them and wire the contacts in parallel, but in this case a single changeover relay/contactor will suffice icon_wink.gif
Back to top
 Alert Moderators
Lectrician

from United Kingdom

Joined: 18 Jul 2004
Posts: 5166
Location: Devon,
United Kingdom
Thanked: 20 times

PostPosted: Sun Jul 23, 2006 7:58 pm    Post Subject:
Reply with quote Thanks

Or you could simply and easily use double pole pull cords - one pole to switch the light, and the other pole to switch the fans sw-live. Fans pem live as normal.

Easy - this is how it is commonly done in commercial apps with a large heat-exchanger type fan ducted between gents/ladies/disabled etc.
Back to top
 Alert Moderators
RMS

from United Kingdom

Joined: 08 May 2006
Posts: 409
Location: United Kingdom
Thanked: 1 time

PostPosted: Sun Jul 23, 2006 8:08 pm    Post Subject:
Reply with quote Thanks

Lectrician,

good idea, but would that mean you would have two supplys in the shower switch?

Nothing wrong with this ofcourse as long as it is clearly identified.

RMS
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
bathroom switches inside or out.? 25 1100 Wed Mar 28, 2007 9:18 am
Bathroom light switches - 1 or 2 way? 6 180 Wed Jan 07, 2009 1:35 pm
12v and 240v bathroom lights/switches - Is is possible? 16 800 Tue Apr 10, 2007 9:38 pm
Move light and shower switches to outside bathroom 13 660 Tue Jan 15, 2008 10:17 pm
Replace wall switches in bathroom cupboard? 8 520 Tue Apr 15, 2008 8:18 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.