earth to neutral short

This topic originated from the How to page called Identifying a faulty circuit
Click here to return to the page called Identifying a faulty circuit.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
markthebuilder

from United Kingdom

Joined: 11 Sep 2006
Posts: 95
Location: Durham,
United Kingdom
Thanked: 0 times

PostPosted: Mon Sep 11, 2006 11:59 am    Post Subject:
earth to neutral short
Reply with quote Thanks

I checked granneys 100a/80a 30ma split load consumer unit to see if it could take additional mcb for Shower.Noted Cooker circut wasn't RCD protected so shifted mcb & neutral to that side. But 80amp RCD wouldnt reset so took out wires again and tested with multimeter which showed a short neutral to earth.
I put back as was with Cooker not RCD protected and all work ok but I have now turned off cooker at mcb as don't want a dangerouse situation
Is neutral earth fault acceptabel?
should cooker be RCD protected?
What is maximum load on an RCD/ incomer ? eg 4x32a +1x45 =173a
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Mon Sep 11, 2006 12:19 pm    Post Subject:
Reply with quote Thanks

Cookers are not usually put on the RCD because (1) they are not portable and are seldom caried outside and used in the rain (2) the oven elements, in particular, tend to leak to earth when they get old. There is an annoying problem with some Cooker Control Units having a 13A socket on them. Who knows how that socket might be used?

IF it is just N-E not P-E it is not generally considered dangerous but you might think about having it tested.

Design load on an RCD can be calculated using diversity; BUT remember that the installation will have a suppliers fuse at 100A or 80A usually, so the CU will not be able to draw more than that for long.

Most RCDs are rated at 80A or 100A; some are only 63A. Unless you have an electric shower and some electric heaters (or a cooker) going through the RCD you will probably not reach that.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Short Circuit Between Earth & Neutral 2 920 Mon Nov 29, 2004 9:59 pm
Earth Wire Too Short! 7 320 Fri Aug 14, 2009 8:56 pm
Earth wire is short 9 600 Wed Jan 11, 2006 12:37 pm
Short circuit info 4 1120 Sun May 28, 2006 2:44 pm
cable to short 2 1560 Wed May 24, 2006 11:58 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.