Joined: 02 Nov 2006 Posts: 2 Location: West Glamorgan, United Kingdom Thanked: 0 times
|
Posted: Thu Nov 02, 2006 8:17 pm Post Subject: microbore |
 |
|
hi all,
some of my radiators are hot some are cold,
yet the pipes feeding them are all hot,up to
the valves.the valves are open but it seems the hot water isnt going into the rads just
straight to the return. all working fine yesterday, and ive tried bleeding them today.
very very confused. |
|
namsag

Joined: 12 May 2004 Posts: 7929 Location: United Kingdom Thanked: 59 times
|
Posted: Thu Nov 02, 2006 8:28 pm Post Subject: |
 |
|
Insertion tube that takes flow of hot water to middle of rad from twin entry valve has fallen off if the water is going straight to the return |
|
vanmann

Joined: 02 Nov 2006 Posts: 2 Location: West Glamorgan, United Kingdom Thanked: 0 times
|
|