RCD's and RCBO's...Whats the difference you may ask?

Goto page 1, 2, 3  Next
 
Post new topic   This topic is locked you cannot edit posts or make replies    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
Big_Spark

from United Kingdom

Joined: 20 Feb 2004
Posts: 3434
Location: United Kingdom
Thanked: 1 time

PostPosted: Sat Feb 21, 2004 1:28 am Reply with quote

I read on the other Electrical forum an old discussion about RCD's and American GFI's. In this discussion it was stated that RCD's do not give Overload protection, however I would like to point out that this is wrong, RCD's DO give overload protection, only basic, but it is there.

For example, a 100A 30mA RCD will trip if the difference between the load on the Phase conductors (Live and neutral) exceeds 30mA or if a 30mA or higher current is detected on the CPC (Earth). Further, if the total load being drawn through the RCD exceeds it's maximum rating, then the RCD will trip and disconnect the circuit.

However, and this is where many people get confused by this, a standard RCD does this by electronic determination of the load current via the detection circuitry unlike the MCB's and RCBO's. The torus forming the heart of the RCD has a small detection circuit attached to it via an op amp. The magnetic field detected by this circuit is carefully measured and if it exceeds a certain thresh-hold, as determined by the maximum load rating, then it will disconnect the circuit

To clarify this, RCBO's combine the operation of the MCB and the RCD into one unit. The RCD part operates in exactly the same way as the standard RCD, however for overload protection the RCBO contains magnetic or thermal trips, in good quality units, such as MK, Merlin-Gerin and Hager, the RCBO contains BOTH thermal and magnetic trips, just as an MCB does.

It is these differences that dictate the use of such devices. RCBO's are used to protect individual circuits that need that extra level of safety, but overload protection is still a vitally important aspect, whereas RCD's are useful, in certain circumstances, for replacing Isolators in Consumer units, Distribution Boards etc where effective disconnection may be required in an emergency or for maintenance etc, but overload protection is not required.

I hope this clarifies the difference between these devices, a proper understanding of the devices will certainly help to determine their proper use.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
il78

from United Kingdom

Joined: 06 Oct 2003
Posts: 701
Location: United Kingdom

PostPosted: Sat Feb 21, 2004 10:35 am Reply with quote

I thought you were telling us a joke.......

Any-hoos

Two Neutrons in a bar, one of them asks the bar tender for pint of lager then changes his mind to a pint of bitter, then changes his mind again to lager, bar tender asks him if he is "Positive".....

I crack myself up....... icon_confused.gif
Back to top
 Alert Moderators
Big_Spark

from United Kingdom

Joined: 20 Feb 2004
Posts: 3434
Location: United Kingdom
Thanked: 1 time

PostPosted: Sat Feb 21, 2004 10:50 am Reply with quote

il78 I think you need to get a more interesting job icon_biggrin.gif
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 25246
Location: Cheshire,
United Kingdom
Thanked: 445 times

PostPosted: Sat Feb 21, 2004 11:34 pm Reply with quote

Aren't RCBO's DC sensing, whereas a lot of RCD's are not??
Back to top
 Alert Moderators
Big_Spark

from United Kingdom

Joined: 20 Feb 2004
Posts: 3434
Location: United Kingdom
Thanked: 1 time

PostPosted: Sun Feb 22, 2004 12:36 pm Reply with quote

securespark wrote:
Aren't RCBO's DC sensing, whereas a lot of RCD's are not??


Generally I would say you are correct, to comply with British Standards, all RCBO's must be DC sensing, however with RCD's the picture is two fold as they can be manufactured as DC sensing or Non-DC sensing.

You need to look at the installation carefully to determine the exact type you want, there are many factors to take into account, not least the environment the circuit will operate in.

For what it is worth, I have noticed lately that a number of manufacturers have started refering to Larger DC Sensing RCD's also as Main RCBO's, I suppose this is an attempt to clarify the whole situation and to ensure that Installers pick the correct protective device.
Back to top
 Alert Moderators
ellk9203636nib

from United Kingdom

Joined: 19 Mar 2009
Posts: 1
Location: Fife,
United Kingdom

PostPosted: Thu Mar 19, 2009 4:07 pm Reply with quote

What a lot of crap. since when did an RCD give overlaod protection.
An RCB on it own will give earth fault protection. The magnetic coil senses an imbalance due to the live conductor increasing its current due to an earth fault and trips.
Back to top
 Alert Moderators
ColJack

from United Kingdom

Joined: 16 Feb 2007
Posts: 11773
Location: West Midlands,
United Kingdom
Thanked: 408 times

PostPosted: Thu Mar 19, 2009 4:18 pm Reply with quote

2004 dude.... check the last date stamp next time...

and welcome to the forum...

icon_biggrin.gif

and in line with the above poor joke..

Two neutrons walk into a bar.. one of them asks the bartender "how much for a pint of vodka?", the bartender replies "to you, no charge..."..

icon_rolleyes.gif
Back to top
 Alert Moderators
hairyben

from Morocco

Joined: 06 Oct 2008
Posts: 644
Location: Morocco

PostPosted: Thu Mar 19, 2009 4:23 pm Reply with quote

RCD's DO NOT provide overload protection.

Whether or not this circuit you speak of will operate the device under excess load, it's not recognised or listed in 7671 as an overload device, and an RCD should be used in conjunction with suitably rated fuses or mcbs.

Don't mean to shoot you down mate but this is a forum for DIYers, don't want anyone being mislead icon_wink.gif
Back to top
 Alert Moderators
LiamPope

from United Kingdom

Joined: 16 Jul 2008
Posts: 509
Location: Bedfordshire,
United Kingdom
Thanked: 20 times

PostPosted: Tue Jun 29, 2010 9:18 pm Reply with quote

Out of interest, was that OP true (in 2004, or even now) or a load of bollarks?
Back to top
 Alert Moderators
holmslaw

from Vanuatu

Joined: 12 Dec 2006
Posts: 5844
Location: Vanuatu
Thanked: 400 times

PostPosted: Wed Jun 30, 2010 8:24 am Reply with quote

He was wrong.

I typed a long explanation but some how deleted it.
Back to top
 Alert Moderators
Risteard

from Ireland

Joined: 18 Jun 2010
Posts: 498
Location: Ireland
Thanked: 32 times

PostPosted: Wed Jun 30, 2010 9:28 am Reply with quote

It was wrong on several counts.

He referred to "live and neutral" as "phase conductors". That should have been phase and neutral being live conductors. (Now line and neutral since the 17th Edition came out.)

He also referred to difference between RCDs and RCBOs. RCBOs ARE RCDs, and as such it follows that some RCDs (namely RCBOs) provide overload protection.

RCCBs do not.
Back to top
 Alert Moderators
ricicle

from United Kingdom

Joined: 14 Sep 2006
Posts: 6308
Location: Gloucestershire,
United Kingdom
Thanked: 377 times

PostPosted: Wed Jun 30, 2010 9:34 am Reply with quote

An RCBO is an RCBO not an RCD (although it does incorporate an RCD)

The RCBO has two parts an RCD and and MCB.

It is the MCB part providing overload protection, not the RCD part - hence some RCDs DO NOT provide overload protection and to say such will only confuse those trying to understand the difference.....
Back to top
 Alert Moderators
Risteard

from Ireland

Joined: 18 Jun 2010
Posts: 498
Location: Ireland
Thanked: 32 times

PostPosted: Wed Jun 30, 2010 9:39 am Reply with quote

ricicle wrote:
An RCBO is an RCBO not an RCD (although it does incorporate an RCD)


An RCBO most certainly IS an RCD.

Look up Definitions (Part 2).
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 48189
Location: London,
United Kingdom
Thanked: 1809 times

PostPosted: Wed Jun 30, 2010 10:10 am Reply with quote

But that does not mean that an RCD provides overcurrent protection.

Look up Definitions (Part 2).
Back to top
 Alert Moderators
Risteard

from Ireland

Joined: 18 Jun 2010
Posts: 498
Location: Ireland
Thanked: 32 times

PostPosted: Wed Jun 30, 2010 10:14 am Reply with quote

An RCBO is an RCD and provides integral overcurrent protection, ergo certain types of RCD do provide overcurrent protection like I said. This does not imply that it is the RCD function of the RCBO providing it, of course.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   This topic is locked you cannot edit posts or make replies    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2, 3  Next
Page 1 of 3

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
whats the difference with all the Mk RCBO models? 3 160 Tue Jan 08, 2013 11:40 am
Flourescents fittings t8 and t5, whats the difference? 5 180 Mon Sep 09, 2013 5:48 pm
Whats the difference? 5 2820 Fri Mar 04, 2005 9:15 am
SP or DP sockets - Whats the difference? 44 36120 Fri Aug 03, 2007 5:59 pm
WHATS THE DIFFERENCE BETWEEN TNS and TNC-S 12 12180 Thu Jun 25, 2009 3:53 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.