DIYnot
Local | Network
   DIYnot > Forums
Local | Network
  Forum IndexForum Index     RulesRules    HelpHelp     Join FREERegister Free     BookmarksBookmarks     Watched TopicsWatched Topics     SearchSearch     LoginLogin
testing
This topic originated from the How to page called Types of electrical circuits
Click here to return to the page called Types of electrical circuits.
  View previous topic :: View next topic
Author Message
oharaf
from United Kingdom
Thanked: 4 times
PostPosted: Thu Jan 18, 2007 9:01 am    Post Subject:
testing
Reply with quote Thanks
HOw can you tell from testing results the difference between a radial circuit and a final ring circuit?
Back to top
 Alert Moderators
If you don't want to see this advert, click here to login or if you are new click here to join free.
EddieCurrent
from United Kingdom
Thanked: 0 times
PostPosted: Thu Jan 18, 2007 9:30 am    Post Subject:
Hello,
(I'll have a go, icon_eek.gif)
r1 + r2 ,rn 'readings' are only possible on 'a1' ring main circuits ????.
Hows that for starters ?
__________________
I suppose I should add the fact that I am not a qualified electrician.
Back to top
 Alert Moderators
oharaf
from United Kingdom
Thanked: 4 times
PostPosted: Thu Jan 18, 2007 9:38 am    Post Subject:
cheers eddie, i'm not qualified YET either, however r1 and r2 are the readings at the socket and the cpc, I don't see how this would distinguish radial from final ring
Back to top
 Alert Moderators
EddieCurrent
from United Kingdom
Thanked: 0 times
PostPosted: Thu Jan 18, 2007 9:51 am    Post Subject:
Hi oharaf,
r1, r2, rn are continuity readings, ( the whole loop), Maybe you are mixing up your R1,R2 and your r1, r2's ?? icon_wink.gif
__________________
Back to top
 Alert Moderators
oharaf
from United Kingdom
Thanked: 4 times
PostPosted: Thu Jan 18, 2007 9:56 am    Post Subject:
Doh! ~Ta take your point to much reading not enough thinking thats my problem!!!
Desperately trying to finish the first 2 years of training within 6 months, so I try to complete the paper work at home and do the practical stuff at college..
Back to top
 Alert Moderators
EddieCurrent
from United Kingdom
Thanked: 0 times
PostPosted: Thu Jan 18, 2007 10:06 am    Post Subject:
I'm sure you'll get there if you keep trying.
Best of luck.
Back to top
 Alert Moderators
RobFurn
from United Kingdom
Thanked: 0 times
PostPosted: Thu Jan 18, 2007 10:24 am    Post Subject:
Are the test results marked on a test cert? If so the test cert has a tick box to indicate its a ring.
However if you unsure the resistance reading obtained at each socket outlet of a ring circuit will be approx 1/4 of the resistance of the phase plus cpc loop resistances i.e. (r1 +r2)/4 look on page 34 of GN3 for more details
Back to top
 Alert Moderators
oharaf
from United Kingdom
Thanked: 4 times
PostPosted: Thu Jan 18, 2007 12:46 pm    Post Subject:
Thanks Rob, the readings aren't on a cert it is an exercise i've to do for college.
The question is;
"Is there any way we can tell from the results recorded, whether a socket oulet is part of the ring final circuit or a spur from the ring?"
Can you help on this one?
Cheers
Back to top
 Alert Moderators
comms
from United Kingdom
Thanked: 0 times
PostPosted: Thu Jan 18, 2007 1:01 pm    Post Subject:
cross connect legs of ring at cu (p/n). now test between p/n at each socket reading should be the same or within 0.05 ohm at each socket (this will be 1/2 the r1 or r2 loop reading) any large rise in reading will be a good indication that the socket will probably be a spur from final ring.
Then do the same with p/e to get your R1+R2.
Back to top
 Alert Moderators
oharaf
from United Kingdom
Thanked: 4 times
PostPosted: Thu Jan 18, 2007 1:11 pm    Post Subject:
That is great comms, I was only doing the cross cenection test last week, but it was only on a ring with no spur.
Would this apply even if the spur was a fused spur?
Back to top
 Alert Moderators
RobFurn
from United Kingdom
Thanked: 0 times
PostPosted: Thu Jan 18, 2007 1:26 pm    Post Subject:
Same for fused spur but of course you cant plug your socket tester in a fused spur so you will have to take the cover off.
The reading is higher as you are distrupting the measurement of the ring by measuring from a spur off the ring
Back to top
 Alert Moderators
oharaf
from United Kingdom
Thanked: 4 times
PostPosted: Fri Jan 19, 2007 11:22 am    Post Subject:
Thanks for your help, AGAIN!
Back to top
 Alert Moderators
Display posts from previous:
Page 1 of 1
Jump to:
Testing ; 13 480 Tue Apr 08, 2008 8:22 pm
TESTING 5 280 Sat Apr 05, 2008 1:41 pm
Practical inspection and testing on rig 19 1000 Sat May 03, 2008 4:34 pm
Testing a socket for a spur... 3 340 Mon May 05, 2008 9:47 pm
testing methods 12 600 Sun Jun 01, 2008 11:39 pm
DIYnot
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum