Sub Meter Protection?

This topic originated from the How to page called Routing cable
Click here to return to the page called Routing cable.
Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
mossiejdm

from United Kingdom

Joined: 14 Feb 2007
Posts: 6
Location: London,
United Kingdom
Thanked: 0 times

PostPosted: Wed Feb 14, 2007 6:18 pm    Post Subject:
Sub Meter Protection?
Reply with quote Thanks

Hi, I have just had a new Crabtree consumer unit professionally installed, 100a main switch, split load 63/30ma RCCB protecting all supplies except lighting. (House built 1960\\\'s)
My query is although the supplier protection fuse is rated at 100A,and fitted between the meter and CU, the suppliers sub meter (ELGEE Type CL7) has 40A max current displayed, how is this arrangement suitable to protect the meter, or is it using a shunt?
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12856
Location: Yorkshire,
United Kingdom
Thanked: 22 times

PostPosted: Wed Feb 14, 2007 8:46 pm    Post Subject:
Reply with quote Thanks

Are you saying you have a meter, then a mainfuse, then another meter? icon_confused.gif

There first thing, on the end of the supply cable, should be a mainfuse/cutout unit.

Then comes a meter. These are often underrated, its nothing to worry about to be honest.

After the meter is your setup, and this can vary. Landlords, for example sometimes fit another meter, a coin meter, to charge tennants for their electric. Generally there will be only one meter. Can you post a picture of your setup for us, showing the whole intake, meter and mainfuse area?
Back to top
 Alert Moderators
mossiejdm

from United Kingdom

Joined: 14 Feb 2007
Posts: 6
Location: London,
United Kingdom
Thanked: 0 times

PostPosted: Wed Feb 14, 2007 10:14 pm    Post Subject:
Reply with quote Thanks

Hi Crafty, second time posting, have uploaded pic of setup i was referring to but not sure when Diynot.com will upload, soon hopefully.

As you correctly stated, from the main service supply cable is the service fuse, (presumably 60-80A?) then looped to the 40A rated sub meter, then looped to another fuse box rated at 100A on the lid, then tails to the CU.

I have 100main switch, with split load 63A/30ma RCCB, total MCB rating are as follows : 32A cooker, Shower 32A, Sockets 32A,Sockets 20A,Shed 20A, lighting 6A non RCCB protection.

I want to upgrade the existing shower (7.5kw) to 8.5 kw,replacing 32A MCB to 40A?
Given the total load would it be advisable to upgrade the RCCB to 80A/30ma?

In terms of sub meter current can you explain what you mean by underated?

Many thanks for your advice on this one.
Back to top
 Alert Moderators
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23346
Location: Sussex,
United Kingdom
Thanked: 5 times

PostPosted: Wed Feb 14, 2007 10:17 pm    Post Subject:
Reply with quote Thanks

picture posting is quicker if you use something like photo bucket.

see forum information

__________________
Do you like music Mr Finch?
Forum = Opinions
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Wed Feb 14, 2007 10:19 pm    Post Subject:
Reply with quote Thanks

You can upload the picture yourself by using an image hosting site such as www.photobucket.com


Far too slow tonight icon_cry.gif

__________________
I downlights


Last edited by RF Lighting on Wed Feb 14, 2007 10:21 pm, edited 1 time in total
Back to top
 Alert Moderators
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23346
Location: Sussex,
United Kingdom
Thanked: 5 times

PostPosted: Wed Feb 14, 2007 10:20 pm    Post Subject:
Reply with quote Thanks

too slow RF Lighting, too slow icon_lol.gif

__________________
Do you like music Mr Finch?
Forum = Opinions
Back to top
 Alert Moderators
mossiejdm

from United Kingdom

Joined: 14 Feb 2007
Posts: 6
Location: London,
United Kingdom
Thanked: 0 times

PostPosted: Wed Feb 14, 2007 10:44 pm    Post Subject:
Reply with quote Thanks

Hi Guys, taken your advice ref photobucket , have posted pic of the the setup via following link....


http://i179.photobucket.com/albums/w309/mossiejdm/Dscn2045.jpg
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12856
Location: Yorkshire,
United Kingdom
Thanked: 22 times

PostPosted: Wed Feb 14, 2007 10:48 pm    Post Subject:
Reply with quote Thanks

That meter is old. Any dates stuck to it? They are ment to be changed every 20 years.
Back to top
 Alert Moderators
mossiejdm

from United Kingdom

Joined: 14 Feb 2007
Posts: 6
Location: London,
United Kingdom
Thanked: 0 times

PostPosted: Wed Feb 14, 2007 10:55 pm    Post Subject:
Reply with quote Thanks

Just legged it out under the stairs and looked, still has the eastern electricity board label saying it was replaced june 85..... wondering why the registered
sparky did'nt flag that up..? who's cost ?
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Thu Feb 15, 2007 12:09 am    Post Subject:
Reply with quote Thanks

I don't understand why you call it a sub-meter. I can't see that it is subsidiary to any "main" meter.

The Earthing arrangements look poor. I can't see evidence of main bonding and I can't see if there is a conductor sweated or clamped onto the sheath.

The tails into the meter are clumsily terminated.

If you write to your supplier and ask them if they will install PME, they probably will, maybe free, maybe for £50/£100. If you tell them the meter rating and tell them your design current, they may provide you with a newer meter too, and hopfully better tails. there should be no charge for swapping the meter.

You could check the main bonding yourself; whoever fitted the new CU ought to have done it but you are permitted to do it yourself as a DIY job. However, do not try to clamp or sweat anything to the cable sheath, and do not tighten the existing clamp as it may damage the cable.

p.s. is that a lead gas pipe underneath? Is it bonded?

p.p.s. Opinions differ on having so many circuits through the RCD. What are they?
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16485
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Thu Feb 15, 2007 3:28 pm    Post Subject:
Reply with quote Thanks

It's a bit of T & E, I think, John!

The main earthing conductor seems to be sweated onto the cable sheath & wrapped in tape. They have (very sensibly) abandoned the EC14...

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Thu Feb 15, 2007 3:30 pm    Post Subject:
Reply with quote Thanks

? look at the size of it compared to the T&E top left. I can also see an anaconda bottom left.
Back to top
 Alert Moderators
davy_owen_88

from United Kingdom

Joined: 17 Nov 2006
Posts: 1680
Location: West Glamorgan,
United Kingdom
Thanked: 0 times

PostPosted: Thu Feb 15, 2007 3:46 pm    Post Subject:
Reply with quote Thanks

Pretty sure it is twin and earth, probably 10mm^2. You can see it's been pulled through a hole and has those scuff marks. And it looks huge because it's so close to the camera:



I don't like the way it's just hanging there though... is it the same piece that is coming from the top of the CU?

Davy
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16485
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Thu Feb 15, 2007 4:26 pm    Post Subject:
Reply with quote Thanks

JohnD wrote:
? look at the size of it compared to the T&E top left. I can also see an anaconda bottom left.


I can't see any snake's @rses, let alone an anaconda's... icon_lol.gif


But I would get shot of the DP Henley block, and wire the tails directly into the meter, without stripping back the grey sheath.

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
mossiejdm

from United Kingdom

Joined: 14 Feb 2007
Posts: 6
Location: London,
United Kingdom
Thanked: 0 times

PostPosted: Thu Feb 15, 2007 4:42 pm    Post Subject:
Reply with quote Thanks

Hi JohnD, My mistake for referencing to the main meter as sub...just been onto eastern electricity who have arranged to install an updated meter early march FOC..
Presumably they will install a higher rated meter, which brings me back to my original query how the meter rating is calculated proportional to current loading on main circuit,(Is the shunt involved here?)
You are quite correct spotting the anaconda hanging down 10mm T&E, cable run for upgrade 8.5kw shower but not connected.

RCCB is suppling 32A cooker,32AShower (wish to upgrade to 40A 8.5kw) 32A Sockets,20A sockets, 20A shed power.
Non RCCB 6A lighting circuit

Given the total load would it be advisable to upgrade the RCCB to 80A/30ma, or should i go for RCBO given 17th edition looming?

Just one other point, the professional who upgraded the cu and installed equipotential bonding to gas main failed to notice the abscence of main water bonding.. hey ho down to b&q's..
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Metal protection for exposed meter tails 4 420 Tue Feb 22, 2005 11:38 am
meter tail protection 16 1680 Tue Mar 13, 2007 4:58 pm
Cable protection (domestic garage), use of met-clad boxes 2 380 Fri Feb 09, 2007 11:38 pm
Extending Ring - cable protection 11 480 Fri Feb 02, 2007 10:17 am
what protection is req if 25m tails were run through house 5 400 Mon Feb 12, 2007 3:37 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.