PostPosted: Wed Mar 07, 2007 12:36 pm    Post Subject:
Low heat output
Reply with quote Thanks

I moved into an old house just before Xmas.During a cold spell the central heating did not seem to cope that well in warming the place up, although all the radiators did warm up. the one nearest to the boiler did appear to be the hottest.I was wondering if it might benefit from a new pump ? the Grundfos one has been marked with a date of 1992 . I have no idea how long they should last.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
big-all

from United Kingdom

Joined: 12 Jul 2004
Posts: 5769
Location: Surrey,
United Kingdom
Thanked: 24 times

PostPosted: Wed Mar 07, 2007 12:50 pm    Post Subject:
Re: Low heat output
Reply with quote Thanks

hardyannual wrote:
I moved into an old house just before Xmas.During a cold spell the central heating did not seem to cope that well in warming the place up, although all the radiators did warm up. the one nearest to the boiler did appear to be the hottest.I was wondering if it might benefit from a new pump ? the Grundfos one has been marked with a date of 1992 . I have no idea how long they should last.


heeelllooo and welcome hardyannual icon_biggrin.gif icon_biggrin.gif icon_biggrin.gif

the one nearest the boiler could be the last in the circuit therefore the coolest untill demand drops from the other radiators

you realy need to say what the capacity of the boiler and how many rads you have before somone [not me ] can work out if you have a mismatch


things to check though

that your boilers on full output and is running continuosly till the last radiator is up to or near full temprature

__________________
big all
we are------------------ all still learning
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24297
Location: London,
United Kingdom
Thanked: 191 times

PostPosted: Wed Mar 07, 2007 12:59 pm    Post Subject:
Reply with quote Thanks

Grunfoss pumps can last 30 years if the water is clean so I dont recommend changing it.

You do need to balance the system and you should also see what condition the water is in. It should be clear and not noticeable blackish. A slight straw colour is OK though.

Tony
Back to top
 Alert Moderators
hardyannual

from United Kingdom

Joined: 07 Mar 2007
Posts: 8
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Mar 07, 2007 2:54 pm    Post Subject:
Reply with quote Thanks

Hi
Thanks for the welcome and advice.

I'll open up one of the drain valves under the rads and check the water

first of all.

cheers
Back to top
 Alert Moderators
hardyannual

from United Kingdom

Joined: 07 Mar 2007
Posts: 8
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Mar 08, 2007 12:08 pm    Post Subject:
Reply with quote Thanks

Further update.

I drained each valve under the rads - lots of black silvery water and for some reason quite foamy in places

drained until the water was clear in each case.

so will see how it goes

cheers
Back to top
 Alert Moderators
gas4you

from United Kingdom

Joined: 23 Feb 2007
Posts: 14312
Location: Norwich,
United Kingdom
Thanked: 41 times

PostPosted: Thu Mar 08, 2007 7:04 pm    Post Subject:
Reply with quote Thanks

Sounds like you have drained quite a lot out. I would suggest adding fresh inhibitor to protect system again icon_wink.gif
Back to top
 Alert Moderators
hardyannual

from United Kingdom

Joined: 07 Mar 2007
Posts: 8
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Mar 09, 2007 11:21 pm    Post Subject:
Reply with quote Thanks

gas4you wrote:
Sounds like you have drained quite a lot out. I would suggest adding fresh inhibitor to protect system again icon_wink.gif


aarh hah is that what the foamy stuff was?

thanks, I had better get some


The heating guy at the old house told me to put it in the small tank every couple of years , but I never really knew where it was going.
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Fri Mar 09, 2007 11:26 pm    Post Subject:
Reply with quote Thanks

If there is lots of black, buy a bottle of chemical cleaner and use this first, then flush it out and refill using your inhibitor.

Sentinel and Fernox are good brands.

Read the instructions several times.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Calculate heat output of existing radiators 9 3380 Fri Mar 17, 2006 8:18 pm
Radiator heat output 5 760 Tue Aug 28, 2007 2:55 pm
Radiator heat output 5 3440 Thu Dec 21, 2006 2:17 pm
Understanding boiler MINIMUM heat output 14 1020 Mon Sep 03, 2007 12:39 pm
Heat output 5 240 Sun Jan 18, 2009 11:48 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.