just changed my board to a split load type and sockets were ok for maybe a minute then the rcd tripped and wont reset??  changed the ring circuit to the non rcd protected side and its fine...any ideas???
cheers
Last edited by 1878 on Fri Mar 09, 2007 8:12 pm, edited 1 time in total |
|
| Back to top |
|
|
|
If you do not want to see this advert, click here to login or if you are new click here to join free. |
 |
Adam_151

Joined: 17 Jun 2004 Posts: 5623 Location: United Kingdom Thanked: 118 times
|
Posted: Fri Mar 09, 2007 8:11 pm |
|
|
What are your IR readings for the ring circuit? |
|
| Back to top |
|
|
|
 |
JohnD

Joined: 15 Nov 2005 Posts: 34466 Location: Hampshire, United Kingdom Thanked: 1097 times
|
Posted: Fri Mar 09, 2007 8:13 pm |
|
|
*sigh* |
|
| Back to top |
|
|
|
 |
bernardgreen

Joined: 03 Nov 2006 Posts: 8692 Location: Bedfordshire, United Kingdom Thanked: 576 times
|
Posted: Fri Mar 09, 2007 8:20 pm |
|
|
Did you the change of CU yourself or was it done by an electrician ? |
|
| Back to top |
|
|
|
 |
1878

Joined: 22 May 2006 Posts: 51 Location: United Kingdom
|
Posted: Fri Mar 09, 2007 8:21 pm |
|
|
i havent taken none...right ok
im an apprentice and i know i shouldnt be doing this but my mum asked if i would as we had an old rewireable type..i've done numerous boards in work with no problems...the guy i work with said he'd test it on monday to check everything was ok  clearly its not...please help me out fellas? |
|
| Back to top |
|
|
|
 |
1878

Joined: 22 May 2006 Posts: 51 Location: United Kingdom
|
Posted: Fri Mar 09, 2007 8:27 pm |
|
|
but still now there is nothing at all on the split load side of the cu and it still will not reset  ...even with all power isolated....still will not reset....could it be a faulty rcd??
i'd really appreciate some advice
thanks  |
|
| Back to top |
|
|
|
 |
ch427

Joined: 16 Jan 2006 Posts: 2134 Location: Cardiff, United Kingdom Thanked: 183 times
|
Posted: Fri Mar 09, 2007 8:31 pm |
|
|
are you sure all the neutrals are in the right place |
|
| Back to top |
|
|
|
 |
JohnD

Joined: 15 Nov 2005 Posts: 34466 Location: Hampshire, United Kingdom Thanked: 1097 times
|
Posted: Fri Mar 09, 2007 8:32 pm |
|
|
Well, if the RCD is tripping, you clearly have an earth leakage. Did you look to see if the RCD still tripped when the MCB was off? That will tell you if it is Phase/earth or Neutral/Earth.
Did you UNPLUG all appliances in the ring? That will tell you if it is a wiring/accessory fault or an appliance fault.
Did you try halving the ring? That will help you identify where the fault is on the circuit.
Presumably you have already had a visual search for damaged wiring or accesories, including rodent damage under floors, or water ingress, and have tried disconnecting any outdoor sockets or lamps on the circuit, which are at risk of collecting rainwater.
You have probably realised now why the Installation Certificate includes spaces for a lot of test results, and why replacing a CU is notifiable work. If you say you have done CU replacements at work I presume someone else has been doing the tests. |
|
| Back to top |
|
|
|
|
|
 |
Spark123

Joined: 02 Jun 2005 Posts: 13807 Location: Cumbria, United Kingdom Thanked: 349 times
|
Posted: Fri Mar 09, 2007 8:32 pm |
|
|
You promise your electrician is coming on monday?
Check you have all your circuits in the correct neutrals.
beaten by ch427!!
Last edited by Spark123 on Fri Mar 09, 2007 8:33 pm, edited 1 time in total |
|
| Back to top |
|
|
|
 |
bernardgreen

Joined: 03 Nov 2006 Posts: 8692 Location: Bedfordshire, United Kingdom Thanked: 576 times
|
Posted: Fri Mar 09, 2007 8:34 pm |
|
|
What was there before, I assume it did not have a RCD fitted.
You do have live and neutral from the meter the correct way round. How did move the tails while they were live ?
Do you have the neutral of the ring in the correct neutral bar in the CU
( CU = consumer unit )
If the neutral is in the correct neutral bar then un-plug everything from the sockets.
If the ring still trips the RCD then there is a fault in the wiring which you, together with an electrician with the necessary test equipment and knowledge, will have to find.
If the sockets work on the un-protected side then MAYBE you could leave them on there but in the knowledge that there is a fault. |
|
| Back to top |
|
|
|
 |
JohnD

Joined: 15 Nov 2005 Posts: 34466 Location: Hampshire, United Kingdom Thanked: 1097 times
|
Posted: Fri Mar 09, 2007 8:35 pm |
|
|
| 1878 wrote: | | ...changed the ring circuit to the non rcd protected side and its fine... |
| 1878 wrote: | | ...but still now there is nothing at all on the split load side of the cu and it still will not reset... |
Talk me through that again?
(p.s. I agree about the Neutrals ) |
|
| Back to top |
|
|
|
 |
DESL

Joined: 09 Oct 2006 Posts: 936 Location: Essex, United Kingdom
|
Posted: Fri Mar 09, 2007 8:38 pm |
|
|
| Quote: | | Check you have all your circuits in the correct neutrals. |
And make sure you have the neutral feeds connected to the correct busbar |
|
| Back to top |
|
|
|
 |
1878

Joined: 22 May 2006 Posts: 51 Location: United Kingdom
|
Posted: Fri Mar 09, 2007 8:44 pm |
|
|
| bernardgreen wrote: | What was there before, I assume it did not have a RCD fitted.
You do have live and neutral from the meter the correct way round. How did move the tails while they were live ?
Do you have the neutral of the ring in the correct neutral bar in the CU
( CU = consumer unit )
If the neutral is in the correct neutral bar then un-plug everything from the sockets.
If the ring still trips the RCD then there is a fault in the wiring which you, together with an electrician with the necessary test equipment and knowledge, will have to find.
If the sockets work on the un-protected side then MAYBE you could leave them on there but in the knowledge that there is a fault. |
no rcd before just a wylex old rewireable board..
yes i'm positive the neutrals are in the correct bar because at first all i had on the split load neautral bar was the ring circuit neutral which wer tested for continuity....as i said changed to unprtected side including neutrals and its running fine but the rcd will still not rest with nothing on that side?? |
|
| Back to top |
|
|
|
 |
Spark123

Joined: 02 Jun 2005 Posts: 13807 Location: Cumbria, United Kingdom Thanked: 349 times
|
Posted: Fri Mar 09, 2007 8:45 pm |
|
|
Last edited by Spark123 on Fri Mar 09, 2007 8:48 pm, edited 1 time in total |
|
| Back to top |
|
|
|
 |
1878

Joined: 22 May 2006 Posts: 51 Location: United Kingdom
|
Posted: Fri Mar 09, 2007 8:46 pm |
|
|
| JohnD wrote: | | 1878 wrote: | | ...changed the ring circuit to the non rcd protected side and its fine... |
| 1878 wrote: | | ...but still now there is nothing at all on the split load side of the cu and it still will not reset... |
Talk me through that again?
(p.s. I agree about the Neutrals ) |
ok because i could not reset the rcd i put the ring circiut across to the non proctected side with my lights and immersion....everything has been fine for the last hour....
so with no load on the rcd side it should reset right? but it won't  |
|
| Back to top |
|
|
|
|
|
 |
|
|