PostPosted: Sun Jun 17, 2007 12:40 pm    Post Subject:
Cable routing again
Reply with quote Thanks

My exterior walls are the common plaster on breeze block, then a void and then brickwork exterior. My question is, do I have to recess into the plaster or can I go through the breeze block, up the void and back through the breeze block in the loft? I know it sounds like more work but I really hate decorating!

Any comments folks?

Thanks
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
festa

from United Kingdom

Joined: 06 Feb 2006
Posts: 212
Location: Cheshire,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jun 17, 2007 1:55 pm    Post Subject:
Reply with quote Thanks

No you cant run a cable in between the cavity of the walls as any damp that DOES come through the exterior brickwork/mortar will use the cable to bridge to the interior wall.

__________________
17th Edition..here we come!
You can teach people to re-wire a plug but cant teach them manners.!
Back to top
 Alert Moderators
onzadog

from United Kingdom

Joined: 04 Apr 2007
Posts: 25
Location: Nottingham,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jun 17, 2007 2:11 pm    Post Subject:
Reply with quote Thanks

Thanks for the reply. I'm always willing to learn about such things. I can understand how this might happen but how come the same doesn't happen with the foam that's filling the cavity?

Isn't running a cable in the void the same method as the cables use to get from the consumer unit to the various parts of the house?

Like I say, the reason I'm asking is because I don't know.

Thanks for the help.
Back to top
 Alert Moderators
festa

from United Kingdom

Joined: 06 Feb 2006
Posts: 212
Location: Cheshire,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jun 17, 2007 3:29 pm    Post Subject:
Reply with quote Thanks

Not too sure what the foam is made of but its a formula that damp cannot affect i suppose...good question and an answer im not sure on icon_confused.gif .

As for cables going to and from a consumer unit again they `should not` be run in cavities, they should be run surface mounted to floor/ceiling voids or can be run in conduits screwed to the plaster /inner brick face.

Some new builds ive been learning on recently have sited the consumer units at around 1200mm high on an interior wall and run lengths of 200mm x 50mm trunking at a corner of the house from ground floor to ceiling and 1st floor to roof void,all in one particular corner of the house.

__________________
17th Edition..here we come!
You can teach people to re-wire a plug but cant teach them manners.!
Back to top
 Alert Moderators
onzadog

from United Kingdom

Joined: 04 Apr 2007
Posts: 25
Location: Nottingham,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jun 17, 2007 4:32 pm    Post Subject:
Reply with quote Thanks

On closer inspection, the cable to the consumer unit passes through the block, void and brick to the unit in the porch. I guess this is where a little common sense is applied as there's no real alternative. The unit is at such a height that some go off through the floor space between levels and the others I've found fun up trunking/conduit inside the plaster in the corner of the building (guess that's the 150 mm permissible zone).

Looks like I need to start chipping away at the plaster and thinking about redecorating then!

Pants!

Thanks for your help though.

BTW, how many lengths of 2.5mm T&E can you normally fit it plaster recessed trunking?

Thanks again.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16491
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Sun Jun 17, 2007 9:15 pm    Post Subject:
Reply with quote Thanks

If you've got insulation in the cavity there are two reasons at least why you should not run cables in there.

One: the insulation will cause the cable to warm up, as it cannot dissipate heat as well.

Two: some insulations damage the pvc: they leech the plasticisers out of the pvc, causing the insulation to become hard & brittle.

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
ssray

from United Kingdom

Joined: 21 Sep 2006
Posts: 56
Location: Birmingham,
United Kingdom
Thanked: 0 times

PostPosted: Mon Jun 18, 2007 8:21 am    Post Subject:
Reply with quote Thanks

The foam wil be closed cell so will not allow the ingress of water, a bath sponge will be open cell so it asborbs water.
Ray
If onlt ohms law etc was as easy!!!
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Routing cable through a back box 5 360 Tue Sep 28, 2004 9:30 am
SWA cable routing and fixing 6 360 Thu Jul 30, 2009 3:09 pm
Another cable routing question. 6 460 Sun Jul 22, 2007 5:00 pm
Routing Cable 6 300 Sat Sep 13, 2008 10:08 pm
Shower cable routing 5 2700 Fri Jul 07, 2006 3:30 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.