Joined: 25 Jul 2007 Posts: 5 Location: Tyne and Wear, United Kingdom Thanked: 0 times
|
Posted: Wed Jul 25, 2007 11:19 am Post Subject: oven & hob |
 |
|
Hi, have recently had a new cu fitted & meter tails. Also new double oven (5.5 kw) with a 32amp breaker (trip ?) to a new 45amp ccu with 10 mm cable & 10mm cable to oven.Now want to fit a ceramic hob(6kw) less than 2m from oven. can i use the same new 45amp ccu with a 10mm cable to hob if so will i have to upgrade the 32amp breaker and what too.thanks.
hope iam replying correctly. thanks luminiare and its yes to your question
Last edited by glock on Wed Jul 25, 2007 11:18 pm, edited 1 time in total |
|
luminaire

Joined: 11 Jan 2007 Posts: 700 Location: United Kingdom Thanked: 0 times
|
Posted: Wed Jul 25, 2007 6:35 pm Post Subject: |
 |
|
Yes, you should just be able to get away with it by using a 45A MCB.
I take it you are not contemplating putting both cables into a Cooker Control Unit, but will in fact be using a Cooker Connection Unit? |
|
jaseandwave

Joined: 18 Nov 2007 Posts: 15 Location: Birmingham, United Kingdom Thanked: 0 times
|
Posted: Sun Nov 18, 2007 10:16 am Post Subject: |
 |
|
I'm doing a similar job at the moment. CCU is about 1m from the hob single oven is about 6m away.
Can I get away with with 6mm cable from 45A breaker in the consumer unit to the CCU, 6mm from ccu to the hob and 6mm from ccu to the oven?
Hob is AEG 68002 induction hob, but I can't find out the wattage. oven is electrolux eob63100x, again, I dont know the wattage but it's nenergy rated A - if that's relevant. |
|
Steve

Joined: 15 Apr 2005 Posts: 12845 Location: Yorkshire, United Kingdom Thanked: 21 times
|
Posted: Sun Nov 18, 2007 2:32 pm Post Subject: |
 |
|
The oven will have a wattage on it somewhere. The rating plate is normally on the back, or on the frame when you open the door. Again, the hob will have a rating on it somewhere - probably underneath or on the sides. Electrolux's website is the worst website I think i've ever had the pleasure of visiting unfortunately.
If the oven is less than 3kw (normal on single ovens), it can be simply plugged into a socket, as it uses no more electricity than a kettle or a heater. Your hob will certainly need a large supply, but if the circuit only supplies the hob, downrate the breaker for 32 amps. Your cooker switch is not "qualified" to control the oven as well, as it is more than 2 metres away.
Install a double pole 20 amp switch on the ring main, controlling a single socket behind the oven (IF, again, its under 3kw) |
|
jaseandwave

Joined: 18 Nov 2007 Posts: 15 Location: Birmingham, United Kingdom Thanked: 0 times
|
Posted: Mon Nov 19, 2007 6:23 pm Post Subject: thanks steve. |
 |
|
I haven't actually got the oven and hob yet so I don't know the output. the oven is A rated for efficienct though - if that means anything. |
|
Steve

Joined: 15 Apr 2005 Posts: 12845 Location: Yorkshire, United Kingdom Thanked: 21 times
|
|