As I typed above, if you have a 15A BS3036 then you must use cable capable of carrying 15/0.725 which works out to around 20.7A. You don't mention if you have thermal insulation surrounding any cables the above is based on not.
1.5mm2 (if indeed your circuit is wired in 1.5mm2 cable) won't carry 20.7A at 30 degree's Celsius so I would suggest changing your 15A fuse to a 10A fuse (assuming no thermal insulation).
If your current loading, after applying diversity, is over 10A then you should be looking to split the circuit.