Recent content by snb1

  1. S

    Unused coil in hot water tank

    if its indirect just leave it un connected. ( it is purely an independant coil) if this is an unvented cylinder then you should be working on it as you need to have a current G3 qualification as it is deemed as dangerous as gas
  2. S

    Confused As Hell - Boilers

    remember diversity (BS6400-1 only applies if more than 2 appliances fitted )for combi boilers is 0.8 , cookers is 0..4 30*08 11*0.4 24*.8 that only equates to 47.6kw so well within spec
  3. S

    CH on continuously

    Yes it will be trying to preheat the hot water but sending it round the rads and the Dhw plate.
  4. S

    Worcester Bosch System Boiler - Best pump settings?

    You can manually select pump speeds 1 to 6 but pump,speed A and B are only used in the auto function. Problem is to get pump pressure of A would require a free flowing primary circuit. My guess is that system will have 22mm primaries. If that is the case then the boiler would only ramp up to...
  5. S

    Worcester Bosch System Boiler - Best pump settings?

    the option of A and B is not selectable. If your system is not getting all the rads hot and it is also new it could be that you still have some airlocks. I would recommend that you change the pump speed to option 6 ( highest available). And then close all the rads. open 1 rad at a time with...
  6. S

    Brand new heating system

    10mm pipe can supply up to 4kw of heat.
  7. S

    Good brands of unvented cylinder

    Because the internal baffle had failed. If you replace with an oversized expansion vessel they last much longer
  8. S

    Good brands of unvented cylinder

    Have fitted loads of external,expansion vessels on mega flows and they have continued to be in use. Some of them I did over 15 years ago and still working
  9. S

    Santon Premier - Vibrating noise

    Replace expansion vessel
  10. S

    Grant Vortex pro 21 Oil Boiler Central Heating Issue

    turn off isolator on heating pump. Leave hot water on. Put hand on heating return pipework. Open the valve you have just closed and you may feel the return pipework get hot . If it does it means the non return valve is not working and allowing reverse circulation.
  11. S

    Question regarding LPG quantity and usage...

    never rely on the auto switch over valve as it will switch over when you still have upto 5% left. even more if the temp is cold. leave the bottles turned off on 2 until you run out and then switch them on.
  12. S

    Riello burner

    you have altered the burner to the completely wrong settings. those are for a non bx burner head. you need to alter to these. 0.75/80/eh nozzle 10.3 bar/150psi oil pump pressure combustion head depth at 19mm. you have to use the special tool to set this air shutter start at 4.25 and...
  13. S

    Grant Vortex pro 21 Oil Boiler Central Heating Issue

    it could be tha, but you don,t get heat leaking out past it. It draws cold water from heating back down it and cools the exchanger. Easy test is to turn the pump isolater off and see if it stops the hot water from trying to reheat
  14. S

    Riello burner

    These semi blue flame burners can be setup wrongly even with an analyser. There are a number of potential issues with the setup. You have changed the photocell? Put the old one back in as a guess you have fitted the wrong type. Send us some updated pictures of it all cleaned. Main exchanger...