So, just to be clear in my own mind, the U/stairs will run on its own, is that correct?.
If so can you take two sets of readings as requested
I am trying to see if the u/stairs heat demand is the same or more (when running on its own) than the d/stairs
How do I get the boiler temp and return temp ?Thanks, but can you also give me the total of the U/stairs flowmeter flow rates as well as that manifold temperature, I can then calculate the UFH demand with the U/stairs running on its own.
Also, if available, the boiler flow temperature and boiler return temperature.
My oil fired system has three motorised valves... one for Hot Water tank, one for the UFH down and a third for the Radiators upstairs.
This system may have similar valves, somewhere for the two heating zones, at least?
My suspicions here are that the UFH is calling for heat (UFH control box 'boiler on'), motoring the valve open but the end microswitch isn't making... and hence not firing the boiler to heat water. When upstairs calls for heat the up valve motors open and the microswitch in that up valve fires the boiler to heat both circuits.
Are you sure. Your post #3 possibly suggested the boiler ran with UFH call only see post #40... if it did not and was just the lamp on the manifold control box, then...Yes that’s what’s happening so how do I fix ?