    Moving a consumer unit

    Just to add there is already a cut out switch by the main fuse
  2. W

    Moving a consumer unit

    Thanks for the replies. The switch's are plastic back box's are metal. The tails will be cut shorter because it will be closer to the main fuse. I literally want to move it 4 inch's
  3. W

    Moving a consumer unit

    I need to move a consumer unit onto the opposite side of a wall where it is currently situated. The circuit wiring will all be cut shorter so no extensions to the circuits will need to be added. The consumer unit is a plastic one in good condition. The lighting circuit is earthed but not to the...
  4. W

    Roof issues with marley modern smooth interlocking tiles

    Hi. I'm currently doing a small pitched roof with a roof window. The tiles are marley modern smooth and the roof window is a sunlux with a universal flashing kit. It abuts to a wall where I have used a grp secret gutter. Firstly the flashing kit is causing me a head ache because it is causing...
  5. W

    RCD test fault

    Yea. oh well ive got new leads on order!!
  6. W

    RCD test fault

    I had the tester calibrated at a different place last year and they told me i needed new leads which are now the faulty ones. So they must have tested my leads then
  7. W

    RCD test fault

    There isnt a fuse. I did suspect these leads were faulty a few weeks back i had a few dodgy readings on an insulation test but when it came back from the calibration with everything ok I obviously thought they were ok.
  8. W

    RCD test fault

    I believe i may have found the issue. I changed my test leads for another pair and it wasnt working just i got the 1999ms reading yet 2 minutes ago with the different leads it tripped fine.
  9. W

    RCD test fault

    Ive just done a x5 test on another house im at with the same tester and it was perfect 12ms ?
  10. W

    RCD test fault

    my meter was only calibrated and tested last week so i would hope itl is in working order
  11. W

    RCD test fault

    Yea sorry it just read 1999 which i just presume to be ohms because thats the reading i get when i do my insulation resistance tests. I had a faulty rcd before that didnt trip and it came up with an error exceeding 500ms maximum limit. so thats why i wasnt sure with this error
  12. W

    RCD test fault

    Ive got a zs on a 6mm cooker radial circuit of 0.27 Immersion heater circuit with 2.5mm radial of 0.15 2.5mm ring circuit of 0.40 Im using a telarus unitest 0100 multi function tester
  13. W

    RCD test fault

    Its a PME with a ZE of 0.07ohms
  14. W

    RCD test fault

    they were still connected but I turned the mcb's off
  15. W

    RCD test fault

    Hi I was testing 2 new rcd's yesterday on a split consumer unit. They are bs-en type the first one tripped in 23ms and the 2nd tripped within 25ms but when i tested x5 i was receiving 1999ohm error? I tested them at the consumer unit and still got the same error. The test buttons...