my combi 105e is acting up just noticed when we ask for hot water via tap or shower head at times the water will go a little cold but i have noticed a small Rad in the bathroom warms Up ? and the rest of my rads are cold as i have not asked for via the room stat for heat ? any help please
 
Sponsored Links
Diverter valve passing to heating circuit. Easy fixed with a valve overhaul.
CHeers for your reply i fitted a overhaul kit, Pin and diaphragm a couple of months ago as water was leaking out the pin hole near to micro switch could be i did not fit it correctly or diaphram has a hole ?
 
Sponsored Links
Diverter valve passing to heating circuit. Easy fixed with a valve overhaul.
CHeers for your reply i fitted a overhaul kit, Pin and diaphragm a couple of months ago as water was leaking out the pin hole near to micro switch could be i did not fit it correctly or diaphram has a hole ?

are ya sure ya didn't fit a overhaul kit to the differential valve and not the diverter?
 