17ed Wiring Changes

Joined
15 May 2007
Messages
212
Reaction score
1
Location
Hampshire
Country
United Kingdom
Hi Guys,

Just had my council's electrical subcontractor round to get a feel for the rewire I am undertaking and he basically said when the 17ed comes into effect in July (I think), ALL cables (unless 50mm deep in the wall) will have to be protected to the same standard as the existing non-horizontal/vertical drops (eg diagonal)- eg using earthed steel conduit.

Is this really correct - sounds wrong to me!

He did say the as I have started the work under the 16ed, I will only have to comply with the 16ed.
 
Sponsored Links
Cables less than 50mm deep, not mechically protetced and not surrounded by an earthed screen suitable for use as a CPC, are still allowed providing they are within prescribed zones (and additionally for the 17th, protected by a 30ma in installations not under supervision of skilled folk)

So, what it means in reality, is a load of new designs of board comming out that have two banks of RCD protected MCBS (and an unprotected way for an RCBO for the smokes)
 