Anyone know if 2 x 6mm T&E cable fits in a 25mm conduit ?
Straight, or are there any bends?Anyone know if 2 x 6mm T&E cable fits in a 25mm conduit ?
Straight, or are there any bends?
Dont know for sure, but if both flat i quess they would, it also depends how long the pipe is
What reg is that, the only one i know relates to space facter not cable sizeA couple of bends.
although i just been informed regs doesn’t allow more than 2 x 2.5mm in a single conduit?
What reg is that, the only one i know relates to space facter not cable size
No chance.A couple of bends.
No chance.
The only way that could happen is if someone shoehorned the cables into the conduit while the conduit was being assembled, which is entirely the wrong thing to do.
Won't comply anyway as T&E cables crammed together in conduit will have a significantly reduced current rating.
10metres and 2 bends seems a bit odd, do they need to be in conduit
10metres and 2 bends seems a bit odd, do they need to be in conduit
T&E cable is not suitable for burial, including when in conduit.Plan is to dig up the path from box to fence.
T&E cable is not suitable for burial, including when in conduit.
That's obviously the official answer, and the advice we must give.T&E cable is not suitable for burial, including when in conduit.