Firstly before you buy the 3 core you can determine wether or not the armour is sufficient to act as the CPC (or bonding conductor etc), either by 54G OR the adiabatic. If the armour on a 2 core is sufficient then why buy 3 core?Fattony said:At what point do you stop using 3 core and start running a seperate cpc?
1) So that you don't have to rely on the integrity of the armour, either the quality of its connection via the glands, or its long-term condition if any water gets in and rusts it?Spark123 said:If the armour on a 2 core is sufficient then why buy 3 core?
Good point.Spark123 said:Wouldn't the armour comply with being used as part of a main equipotential bond as long as its csa is greater than 10mm² copper equivalent (providing 10mm² acceptable by DNO)?