- Joined
- 11 Jan 2004
- Messages
- 42,768
- Reaction score
- 2,641
- Country
I knew as soon as I left the house without my K800i that it would be a good day for pictures.
And yet more mails in the coffin of my opinion of the NIC.
Went to inspect a domestic install today in a very smart area of Cheshire, footballers & all that...the customer was expecting a clean bill of health as he had had "a senior NICEIC inspector" to replace the fuseboard.
It was a wee bit odd in that the PME intake was in a detached garage. This then went (in 16mm² tails) to a large metal Bill 100A isolator, then onto a fuse cabinet feeding two heating contactors & timeclocks and a hefty run of galv trunking.
This was all quite badly corroded.
The MEB to the gas was undersized & on the cast supply pipe.
There was no visible MEB to the water pipe.
The sub-main to the house was run in PVC coated MICC., with no visible means of fusing down or isolation at the supply end.
The MICC was terminated into a metalclad CU (into an oversized hole)with no banjo oe additional earthing conductor (is the sheath of 6/10mm² MICC sufficient to be used as the supply earth?).
There was no sign of any EIC and there were loads of small scary bits like a external flex to a pump that was so perished, the cpc & neutral were exposed & a conduit box lid missing in the garage, with exposed connectors hanging out of it. And a high Zs in the kitchen, too.
This "NIC inspector" had changed the board having noticed the bonding was up the creek, commented to the householder that is was wrong, but had gone ahead with the work anyway...
The other job was a board change & new DB in the garage done by an NIC DI, all nicely labelled up with "NICEIC DI" stickers and marked "DB1" and "DB2".
But no EIC, no name, address or phone number.
The RCD incomer board in the house had two 32A breakers feeding 3x 2.5 radials, 2 on one and one on the other. There was no MEB to the water.
The garage DB was fed in 1.5mm² SWA (from one of the 32A breakers), and the SWA was just poked into the CU, with the conductors showing on the outside.
This was a pic I took on a previous visit:
Good, hey?
Good, hey?