I think my automatic by-pass valve is stuck on my S plan heating system. No matter what setting I have it on (fully open/ fully closed) it looks like water/heat is going through it.
I have tried from system cold turning on zone 1+2 heating and the boiler return feed is a lot hotter than either of the zone returns even with the bypass set to closed (0.5 bar).
Does this sound like the valve has failed or is the value just not restrictive enough?
Current bypass: Danfoss ARV22
Pump: Grundfos UPS025-60-130 P/N:97781518
Boiler: Glow worm Flexicom 12hx
If I get a replacement I was trying to work out what I should set the new valve too however I was struggling to find the minimum flow rate of the boiler and pump curves.
Nearest pump curves I could find were:
https://product-selection.grundfos....tid=GMA&productnumber=96281480&qcid=755334215
The pump has a sticker on it saying:
Q= 1.0m3/h
H(m3) | P (W) | Speed
5.0 | 78 | 3
3.8 | 70 | 2
1.8 | 59 | 1
I currently run it on speed 1.
Any help on working this out would be appreciated.
Thanks
I have tried from system cold turning on zone 1+2 heating and the boiler return feed is a lot hotter than either of the zone returns even with the bypass set to closed (0.5 bar).
Does this sound like the valve has failed or is the value just not restrictive enough?
Current bypass: Danfoss ARV22
Pump: Grundfos UPS025-60-130 P/N:97781518
Boiler: Glow worm Flexicom 12hx
If I get a replacement I was trying to work out what I should set the new valve too however I was struggling to find the minimum flow rate of the boiler and pump curves.
Nearest pump curves I could find were:
https://product-selection.grundfos....tid=GMA&productnumber=96281480&qcid=755334215
The pump has a sticker on it saying:
Q= 1.0m3/h
H(m3) | P (W) | Speed
5.0 | 78 | 3
3.8 | 70 | 2
1.8 | 59 | 1
I currently run it on speed 1.
Any help on working this out would be appreciated.