Boiler and radiator manufacturers' use delta T to mean different things.
To the boiler manufacturer it is the difference between flow and return temperature. So a Flow of 75C and Return of 55C gives a 20C Delta T (75-55)
To the radiator manufacturer it is the difference between Mean Water Temperature (MWT) and Room temperature. A radiator with flow of 75 and return of 55 has a MWT of (75+55)/2 =65C. If the room temperature is 20C the radiator Delta T is 45C.
As the heat output of a radiator depends on Flow, Return and Room temperatures, all rads have to be tested to a common standard, BS EN442. This specifies Flow = 75C, Return = 65C (MWT=70C) and Room =20C. Hence the rad Delta T of 70-20=50C.
If you want to run at a 20C boiler delta T, you have to take this into consideration when selecting your radiators as the output will be less than that quoted by the manufacturer. There is normally a table in the radiator literature showing the correction factor for different (radiator) delta Ts.
Thanks.
I'm not going to replace my rads to meet the maximum boiler delta, however will work out what my rads are (not sure what brand they are but all have fix stamped in them) and see if they are sized for the delta. If not the system can stay exactly as it is, as it is working the best it has ever worked at the moment, and that's what I'm most fussed about, although if I can get it right then I would prefer to do that.