Baxi constantly firing up when no hot water demand.

Discussion in 'Plumbing and Central Heating' started by stehodgy, 14 Feb 2010.

  1. stehodgy

    Joined:
    14 Feb 2010
    Messages:
    7
    Thanks Received:
    0
    Location:
    Lancashire
    Country:
    United Kingdom
    I have a Baxi Combi 80Eco boiler. It is firing up every 10 seconds or so, stays in for a couple of seconds, goes out and then repeats. This happens when the control is set to DHW/CH and the heaters are warmed up and the hot water tap not turned on and it also happens when the control is set just to DHW alone without any taps being turned on at all. The only time it doesn't fire up is when the control is set to off. Any help would be appreciated.
     
  2. stehodgy

    Joined:
    14 Feb 2010
    Messages:
    7
    Thanks Received:
    0
    Location:
    Lancashire
    Country:
    United Kingdom
    A couple of days ago the diaphragm and pushrod were changed in the DHW pressure diff valve because there was a small leak coming from there, I think the boiler was drained to do this.
     
  3. stehodgy

    Joined:
    14 Feb 2010
    Messages:
    7
    Thanks Received:
    0
    Location:
    Lancashire
    Country:
    United Kingdom
    There might be a need to draw a picture as I'd like to sort it myself. Right, I've been to look at the job he did and looked not only at the DHW diff valve but the CH diff valve. Whichever position the control is in (except off) the pushrod in the CH valve makes the microswitch and doesn't go off even when the hot water is turned on, the only time it doesn't touch the microswitch in the CH valve is when the control is in the off position.
     
  4. ChrisR

    Joined:
    24 Jul 2003
    Messages:
    23,632
    Thanks Received:
    1,155
    Location:
    London
    Country:
    United Kingdom
    SOunds like he might have got water on the PCB. You could try gentle drying with a hair dryer.

    Flame is recognised by a tiny current, which water would interfere with. Boiler thinks flame not lit, so it cuts gas to have another go.

    There's NO pushrod for CH alone, that's for the pump, whioch operates whenevee the boiler's on.
     
  5. stehodgy

    Joined:
    14 Feb 2010
    Messages:
    7
    Thanks Received:
    0
    Location:
    Lancashire
    Country:
    United Kingdom
    Thanks I'll give that a go. I probably should also say that when the heating is put on from cold the flame stays lit until the heaters are warm and then starts firing up every few seconds and doesn't stop. Altho it starts right at the begining when it's just the DHW on when no hot water is required.
     
  6. gas112

    Joined:
    27 Oct 2009
    Messages:
    9,525
    Thanks Received:
    2,396
    Country:
    United Kingdom
    Faulty microswitch . The one the hot water pin activates
     
    • Thanks Thanks x 1
  7. stehodgy

    Joined:
    14 Feb 2010
    Messages:
    7
    Thanks Received:
    0
    Location:
    Lancashire
    Country:
    United Kingdom
    Thanks, is that a job i can do myself possibly?
     
  8. stehodgy

    Joined:
    14 Feb 2010
    Messages:
    7
    Thanks Received:
    0
    Location:
    Lancashire
    Country:
    United Kingdom
    Cheers, I changed it today and it's working properly again.
     
  9. ArnoldJ

    Joined:
    24 Feb 2010
    Messages:
    2
    Thanks Received:
    0
    Location:
    Sussex
    Country:
    United Kingdom
    I have the same problem but alas I'm going to have to call out the plumber because this is way beyond my (poor!) DIY skills. So could someone confirm exactly what part I need to ask them to change? You mentioned microswitch......?

    A plumber did come out to 'look' at the problem and said it might be the PCB and would go away and order one.... I never heard from him again!

    Thanks.
     
  10. weargas

    Joined:
    24 Mar 2004
    Messages:
    632
    Thanks Received:
    14
    Location:
    Tyne and Wear
    Country:
    United Kingdom
    dhw microswitch assy for the eco is what you ask for, it comes attached to a full wiring harness including connections to the pcb, selector switch, terminal strip and pump. You can do a shortcut by cutting the wires of the microswitch and just replacing the switch. I like to do it the proper way:)
    Baxpoti will supply you with a part number as it's not on any of the exploded diagrams in spares suppliers for some reason.
     
    • Thanks Thanks x 1
  11. ArnoldJ

    Joined:
    24 Feb 2010
    Messages:
    2
    Thanks Received:
    0
    Location:
    Sussex
    Country:
    United Kingdom
    Many thanks for such a quick response! I now feel more confident in what I need to ask for. Much appreciated.... :D
     
  12. Agile

    Joined:
    26 Jun 2004
    Messages:
    55,752
    Thanks Received:
    3,671
    Location:
    London
    Country:
    United Kingdom
    Thats typical of someone who does not really know whats wrong!

    Changing the switch and wiring assembly is rather stretching a DIYers capability as its quite involved.

    I cannot advise it but I have seen some people who very simply cut the wires to the switch and just connect the three wires together using a choc block.

    Tony
     