Baxi Solo 2 PF overheat coming on

Joined
1 Nov 2007
Messages
2
Reaction score
0
Location
Berkshire
Country
United Kingdom
Hi,

I need some help with my baxi boiler. I recently fitted a new power shower meaning that I had the boiler switched off for a few days. When I switch the boiler back on it only stays lit (boiler, fan, pilot, burner) for around twenty seconds before it makes some clunking noises and switches off with the overheat light coming on. I've investigated the pipe work and believe the clunking is due to the pipes expanding and contracting as at one point they rest on one another. Restting the boiler does not apear to cure the fault and the boiler remains off. I have bled the top feed to the boiler as I suspected air could be a problem.

any help would be appreciated,

many thanks!
 
Sponsored Links
Check your pump is not stuck and that there is 230V going to it.

If it is not stuck and there is not 230V then I would suspect the pcb as this controls the pump.
 
thanks for you help, I investigated the pump and found it to not be working which I have traced to a loose connection in a junction box! All sorted and working fine- thanks![/list][/quote]
 