hi

problems with baxi solo 3, relay on the pcb chattering without demand, tried new pcb still the same problems,removed fan aps, still same ur reply much obliged thanks.
 
Sponsored Links
If you're compotent
Step 1
Check live, swl and neutral incoming are correct and pump feed out is correct, note readings!
(Isolate power)
Disconnect and isolate your Switched Live swl feed at the boiler terminal
(Power on )
Does it still make the noise at the same time as before?
 
thanks for the reply

i have isolated pump live and switch live, still same problem, phoned baxi. went through faulty finding all reading were ok apart from thermister slightly out of range1.9kohms, was advised to change, so changed still same problem. polarity all ok.
 
Have you checked the voltage between neutral and earth?

Tony
 
Sponsored Links
Rafael said:
hi

problems with baxi solo 3, relay on the pcb chattering without demand, .


What do you mean by no demand?
What diverter do you have?
 